There you go - just a rated partition and not a fire wall.

I'll either have to call Ken - John Jr or just reference having the  
code boys to get'er done

Roland

On Nov 5, 2009, at 12:25 PM, Ken Holsopple (forum) wrote:

> Roland -
>
>> From the IRC 2006
>
> Under Section R317 Dwelling Unit Seperation
>
> R317.2 Townhouses.
> Each townhouse shall be considered a separate building and shall be
> separated by fire--resistance-rated wall assemblies meeting the  
> requirements
> of Section R302 for exterior walls.
>
> Exception: A common 2-hour fire-resistance-rated wall is permitted for
> townhouses if such walls do not contain plumbing or mechanical  
> equipment,
> ducts or vents in the cavity of the common wall. Electrical  
> installations
> shall be installed in accordance with Chapters 33 through 42.  
> Penetrations
> of electrical outlet boxes shall be in accordance with Section R317.3.
>
> R317.2.1 Continuity.
> The fire-resistance-rated wall or assembly separating townhouses  
> shall be
> continuous from the foundation to the underside of the roof  
> sheathing, deck
> or slab. The fire-resistance rating shall extend the full length of  
> the wall
> or assembly, including wall extensions through and separating attached
> enclosed accessory structures.
>
> Ken Holsopple