That's pretty much what I told them.

Until this thread came up.

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: david.au...@nebraska.gov
 

-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Joe Burtell
Sent: Monday, November 09, 2009 2:11 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: QR vs SSP sprinklers in LH vs OH delivery

NFPA 13 02'
A.8.3.3.1 When renovations occur in an existing building and no changes are 
made in the existing
sprinkler system, this section is not intended to require the replacement of 
existing standard
sprinklers with quick-response sprinklers.

Might work for you.


Best regards,

Joe Burtell, SET, CFPS
Burtell Fire Protection
Phone: 406.652.7697
Fax: 406.652.7743
Cell: 406.861.4507
Email: j...@burtellfire.com
Web Site: http://www.burtellfire.com
 please don't print this e-mail unless you really need to



-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org 
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Autry, David
Sent: Monday, November 09, 2009 1:03 PM
To: sprinklerforum@firesprinkler.org
Subject: RE: QR vs SSP sprinklers in LH vs OH delivery

I got an old grocery store (OH GR II), which is being bought and turned into 
office space with cubicles (LH).
So according to this thread, they must replace all the sprinklers at the 
ceiling with QR sprinklers.
Seems like an added expense that's not really needed. I can't seem to put my 
finger on the thought that the sprinkler system "knows" what hazard is below 
and what it's protecting. If it's good for OH GP II why would it not be good 
for OH GR I or LH?
Are ya'll trying to say that if they put in a EH water-spray deluge system, in 
this building it wouldn't put out a LH fire?  

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: david.au...@nebraska.gov
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to