"Are ya'll trying to say that if they put in a EH water-spray deluge system,
in this building it wouldn't put out a LH fire?"

See that's where we went astray.  I don't think this conversation was ever
about fire control or suppression.  It is about code compliance.  The two
are sometimes confused.  

If you do not use QR in an LH you are not in compliance with the Code.
Existing exception noted.  

Now if you (a PE) wants to submit an alternate for a EH deluge...code
official...proposed design...complies with the intent...at least
equivalent...quality, strength, effectiveness, fire resistance, durability
and safety they certainly can.  The only area for debate is durability in an
EH deluge.  Is a deluge as durable over time given the complexity?

Want to use SR vs. QR the debate is probably over effectiveness.  Is waiting
for a SR head as effective as a QR head?  Yes, I know it's a matter of
seconds in most cases.  But the wise NFPA committee was convinced there was
a benefit.  No matter how long the difference the fire IS bigger if you
wait.   

So EH deluge or SR I think complies with the intent but maybe lacking in the
list of specific criteria depending on how YOU look at it and the skill of
the PE in convincing an AHJ.  Or that is to say the skill of the AHJ in how
fine they want to split the hair. 

FWIW I would not accept SR OH in a LH when I was AHJ.  I won't say I had a
fancy reason based on anything.  But I also never had a crafty PE submit an
alternate.  And I'm not sure what I'd do with the change of use issue you
mention.  Don't recall a similar.   Base code says new so does that override
the NFPA 13 exception?  We'll only know after a loss and the lawyers get
through with it.             

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, November 09, 2009 2:22 PM
To: [email protected]
Subject: RE: QR vs SSP sprinklers in LH vs OH delivery

There ya go, David- common sense and the code coinciding with your initial
reaction. I'd call it a day while you're ahead.

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Monday, November 09, 2009 3:21 PM
To: [email protected]
Subject: RE: QR vs SSP sprinklers in LH vs OH delivery

The question is compliance with the 1996 #13 change requiring QR heads in
light hazard occupancies. Since you have a change in use, I believe that you
could require that.

Course if the salespeople are selling groceries, wouldn't that still
constitute OH 2 mercantile since they're selling the same commodity, albeit
with a different delivery method.

I don't see the problem with an office being deemed OH and not having it
retrofit with QR in a situation like that. There's probably a lot to be said
for a 100% increase in density over minimum, largest impact being whether or
not the ceiling is 12~15; high or >20' high for response time. If I were an
FPE, I'd render an opinion, but I'm not.

We've got older buildings Back East; a LOT of unsprinklered existing stock.
I'd sure spend more time worrying about unsprinklered buildings instead of
this one getting changed to QR IF I were a PE or BCO. Big picture time?

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Autry, David
Sent: Monday, November 09, 2009 3:03 PM
To: [email protected]
Subject: RE: QR vs SSP sprinklers in LH vs OH delivery

I got an old grocery store (OH GR II), which is being bought and turned into
office space with cubicles (LH).
So according to this thread, they must replace all the sprinklers at the
ceiling with QR sprinklers.
Seems like an added expense that's not really needed. I can't seem to put my
finger on the thought that the sprinkler system "knows" what hazard is below
and what it's protecting. If it's good for OH GP II why would it not be good
for OH GR I or LH?
Are ya'll trying to say that if they put in a EH water-spray deluge system,
in this building it wouldn't put out a LH fire?  

David Autry
Plans Examiner
Nebraska State Fire Marshal's Office
246 S. 14th Street
Lincoln, NE 68508
402-471-9659
402-471-3118 fax
www.sfm.ne.gov
 
** Note new email address: [email protected]
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to