I have to agree that all questions of water supply aside, 8.3.4.1 seems pretty 
clear that k4.2 sprinks cannot be used in anything except light hazard 
occupancy. 

Supposing they had used the proper heads...I would reject on the basis that 
they tested a water main that does not feed the building. It seems like they 
may have just fudged the placement a little in order to suggest that they 
probably might have water similar to what was tested.

Supposing they had the right heads and had tested the right line...I would 
approve. Especially if they have knocked 10% off already. The reason that there 
is a cut-off is because you have to be able to say yes or no at some point. 
Obviously more safety is more better, but we can't all drive around in tanks 
wearing football helmets.

My understanding is that the 10% number is just one that was picked out of thin 
air as something that people are generally ok with. I see specs call for 10% 
psi, or 10psi, or 20 (both ways). There are some jurisdictions around here that 
tried to push 30% for a while.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 30, 2009 2:11 PM
To: [email protected]
Subject: Calcs-How much margin

I've got a calc I'm reviewing, after all said and done, 3.63 psi margin between 
demand and available.  Designer used 4.2K heads to get the flow exactly to the 
decimal of the required flow.  This is an industrial type project.  With a .15 
gpm/sf density at 92 sf per head, the flow would be 13.8 gpm and he's dead on 
the money.  The concern would be that over the years if there was any change in 
the water supply or decay of the piping, that the operation of half the design 
area would be questionable.  

Would you approve or reject this design?  Is this cutting it just a bit close?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to