John, 

You mentioned one issue that I had concerns over and that was the fact that 
this project is within a developing industrial area.  As I said there are other 
issues that also contributed to the decision to ask for a resubmittal.

But the fact that the water test was performed on a hydrant that isn't anywhere 
near the project site, well I just can't accept that.  



Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Monday, November 30, 2009 5:22 PM
To: [email protected]
Subject: RE: Calcs-How much margin

Craig,

You've received plenty of comment. Travis and John found the first problem with 
the design, the code section is 2007 NFPA-13-8.3.4. Before one can decide if 
the water supply is adequate the system demand must be validated.
22.2.1 provides the required information for water supply, 22.3.5.4 for supply 
analysis and 23.2.1.2 for determination. 

23.2.1.2 provides the answer; "The volume and pressure of a public water supply 
shall be determined from waterflow test data. An ADJUSTMENT TO THE WATERFLOW 
TEST DATA TO ACCOUNT FOR daily and seasonal fluctuations, possible interruption 
by flood or ice conditions, large simultaneous industrial use, future demand on 
the water supply system, OR ANY OTHER CONDITION THAT COULD AFFECT THE WATER 
SUPPLY SHALL BE MADE AS APPROPRIATE.

As for a prescribed absolute, my understanding pursuant to the standard is 
supply (properly determined) and demand can match, thus nothing implicitly 
saying "adjust by 10%". 

The annex of NFPA-13 does provide insight;  A.23.2.1 "Care should be taken in 
making water tests to be used in designing or evaluating the capability of 
sprinkler systems. The water supply tested should be representative of the 
supply that might be available at the time of a fire. For example, testing of 
public water supplies should be done at times of normal demand on the system. 
Public water supplies are likely to fluctuate widely from season to season and 
even within a 24-hour period. Allowance should be made for seasonal or daily 
fluctuations, for drought conditions, for possibility of interruption by flood, 
or for ice conditions in winter. Testing of water supplies also normally used 
for industrial use should be done while water is being drawn for industrial 
use. The range of industrial-use demand should be taken into account. In 
special situations where the domestic water demand could significantly reduce 
the sprinkler water supply,an increase in the size of the pipe su
 pplying both the domestic and sprinkler water can be justified. Future changes 
in water supplies should be considered. For example, a large, established, 
urban supply is not likely to change greatly within a few years. However, the 
supply in a growing suburban industrial park might deteriorate quite rapidly as 
greater numbers of plants draw more water.

Testing of Water Supply. To determine the value of public water as a supply for 
automatic sprinkler systems, it is generally necessary to make a flow test to 
determine how much water can be discharged at a residual pressure at a rate 
sufficient to give the required residual pressure under the roof (with the 
volume flow hydraulically translated to the base of the riser) - that is, a 
pressure head represented by the height of the building plus the required 
residual pressure. The proper method of conducting this test is to use two 
hydrants in the vicinity of the property. The static pressure should be 
measured on the hydrant in front of or nearest to the property and the water 
allowed to flow from the hydrant next nearest the property, preferably the one 
farthest from the source of supply if the main is fed only one way.

For further information on water supply testing, see NFPA-291, Recommended 
Practice for Fire Flow Testing and Marking of Hydrants. Keep in mind that while 
NFPA-291 is recommended practice and not a standard it nonetheless has bearing 
in jurisdictions that include language such; "Any requirement essential for 
structural, fire or sanitary safety of a building or structure, or essential 
for the safety of the occupants thereof, and which is not specifically covered 
by the regulations, shall be determined by the construction official, and 
appropriate subcode official" (NJAC 5:23-2.2(c)) 

With that you have more than enough justification to reject this application, 
as I would. 

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

PS. It's too late once the fire starts.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, November 30, 2009 3:11 PM
To: [email protected]
Subject: Calcs-How much margin

I've got a calc I'm reviewing, after all said and done, 3.63 psi margin between 
demand and available.  Designer used 4.2K heads to get the flow exactly to the 
decimal of the required flow.  This is an industrial type project.  With a .15 
gpm/sf density at 92 sf per head, the flow would be
13.8 gpm and he's dead on the money.  The concern would be that over the years 
if there was any change in the water supply or decay of the piping, that the 
operation of half the design area would be questionable.  

Would you approve or reject this design?  Is this cutting it just a bit close?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to