Not talking about Craig specifics.  All John/NFPA provides is great except
it should be in AWWA standards not NFPA standards.  These people forget the
water system originally was a fire protection function to keep the town from
burning down.  Even today its flows are FP based not domestic.  Ask a water
guy anything about anything other than GPD and you get a lot of blank
stares. You can't adjust if the water utility doesn't know any of the
stipulated information.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John Drucker
Sent: Monday, November 30, 2009 4:22 PM
To: [email protected]
Subject: RE: Calcs-How much margin

Craig,

You've received plenty of comment. Travis and John found the first problem
with the design, the code section is 2007 NFPA-13-8.3.4. Before one can
decide if the water supply is adequate the system demand must be validated.
22.2.1 provides the required information for water supply, 22.3.5.4 for
supply analysis and 23.2.1.2 for determination. 

23.2.1.2 provides the answer; "The volume and pressure of a public water
supply shall be determined from waterflow test data. An ADJUSTMENT TO THE
WATERFLOW TEST DATA TO ACCOUNT FOR daily and seasonal fluctuations, possible
interruption by flood or ice conditions, large simultaneous industrial use,
future demand on the water supply system, OR ANY OTHER CONDITION THAT COULD
AFFECT THE WATER SUPPLY SHALL BE MADE AS APPROPRIATE.

As for a prescribed absolute, my understanding pursuant to the standard is
supply (properly determined) and demand can match, thus nothing implicitly
saying "adjust by 10%". 

The annex of NFPA-13 does provide insight;  A.23.2.1 "Care should be taken
in making water tests to be used in designing or evaluating the capability
of sprinkler systems. The water supply tested should be representative of
the supply that might be available at the time of a fire. For example,
testing of public water supplies should be done at times of normal demand on
the system. Public water supplies are likely to fluctuate widely from season
to season and even within a 24-hour period. Allowance should be made for
seasonal or daily fluctuations, for drought conditions, for possibility of
interruption by flood, or for ice conditions in winter. Testing of water
supplies also normally used for industrial use should be done while water is
being drawn for industrial use. The range of industrial-use demand should be
taken into account. In special situations where the domestic water demand
could significantly reduce the sprinkler water supply,an increase in the
size of the pipe supplying both the domestic and sprinkler water can be
justified. Future changes in water supplies should be considered. For
example, a large, established, urban supply is not likely to change greatly
within a few years. However, the supply in a growing suburban industrial
park might deteriorate quite rapidly as greater numbers of plants draw more
water.

Testing of Water Supply. To determine the value of public water as a supply
for automatic sprinkler systems, it is generally necessary to make a flow
test to determine how much water can be discharged at a residual pressure at
a rate sufficient to give the required residual pressure under the roof
(with the volume flow hydraulically translated to the base of the riser) -
that is, a pressure head represented by the height of the building plus the
required residual pressure. The proper method of conducting this test is to
use two hydrants in the vicinity of the property. The static pressure should
be measured on the hydrant in front of or nearest to the property and the
water allowed to flow from the hydrant next nearest the property, preferably
the one farthest from the source of supply if the main is fed only one way.

For further information on water supply testing, see NFPA-291, Recommended
Practice for Fire Flow Testing and Marking of Hydrants. Keep in mind that
while NFPA-291 is recommended practice and not a standard it nonetheless has
bearing in jurisdictions that include language such; "Any requirement
essential for structural, fire or sanitary safety of a building or
structure, or essential for the safety of the occupants thereof, and which
is not specifically covered by the regulations, shall be determined by the
construction official, and appropriate subcode official" (NJAC 5:23-2.2(c)) 

With that you have more than enough justification to reject this
application, as I would. 

Hope that helps,

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

PS. It's too late once the fire starts.


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Monday, November 30, 2009 3:11 PM
To: [email protected]
Subject: Calcs-How much margin

I've got a calc I'm reviewing, after all said and done, 3.63 psi margin
between demand and available.  Designer used 4.2K heads to get the flow
exactly to the decimal of the required flow.  This is an industrial type
project.  With a .15 gpm/sf density at 92 sf per head, the flow would be
13.8 gpm and he's dead on the money.  The concern would be that over the
years if there was any change in the water supply or decay of the piping,
that the operation of half the design area would be questionable.  

Would you approve or reject this design?  Is this cutting it just a bit
close?

 


Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to