FM would tell you to go with a 0.25/3,000 on a wet system; 5,000 if dry.  The 
shielded aspect is the big issue - as you point out.  And if the shielded are 
is large enough (highway trailer for instance) then I would think FM's 
protection scheme would make sense.

The 0.15/1,500 has worked inside standard parking garages (autos, SUVs, and 
pickups; low ceilings) and therefore is reasonable - but as Roland implies, if 
this is a large trailer, you have a different beast.

Mark A. Sornsin, PE
Fire Protection Engineer
Ulteig Engineers, Inc.
Fargo, ND
Direct:    701. 280.8591


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Thursday, January 07, 2010 9:26 AM
To: [email protected]
Subject: Re: trailer parked inside

The first and main question I would ask is how long is the truck.  If
it is a tractor-trailer length, go with your plan.  If it is a news
van (such as 15 ft) that's a different story.

Roland

On Jan 6, 2010, at 5:54 PM, Todd Williams wrote:

> I am looking at a project where a company will back a full size
> trailer into a building and retrofit it with electronic equipment
> (think big mobile news truck). Only one trailer will be in the
> building at a time. The rest of the facility will be electronic
> assembly and 14 ft rack storage of electric equipment. I'm thinking I
> have to look at this as extra hazard group 2 (similar to manufactured
> home assembly - due to the shielded fire potential). I am getting a
> lot of resistance from the architect, contractor and the owner that
> it is not that severe since it is only one truck and only occupies
> 10% of the space. The space is wide open with no enclosures. Am I on
> target with this or over-engineering yet again?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, Connecticut
> www.fpdc.com
> 860.535.2080
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to