At least the few I have been involved with are designed for fire safety in
mind with truck shows or boats...Some don't even have sprinklers above the
main display area especially when over 200'.  So very large fires are
anticipated and people are dealt with safely.  For example no one is allowed
above the main concourse when there is a combustible show on the event
floor.  The structure is not in jeopardy.  If all this applies to Todd's
case then great, sprinklers don't matter. Older convention centers yeah they
probably are OHII but that doesn't make it the right density. 

I'd play it IMHO it is EXII over the area and leave the final decision up to
the AHJ and owner. As long as you are on record you should be safer if
anything goes wrong.   

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Thom McMahon
Sent: Thursday, January 07, 2010 10:46 AM
To: [email protected]
Subject: RE: trailer parked inside

Anyone ever been to one of those Auto or truck shows for big rigs? There the
fuel load is enhanced by all the lighting and displays, carpet ect. What
would you protect an auditorium with? Is your roof deck 100'-0" AFF? .3/2000
for the storage? I see no great difference in your single trailer issue? Do
you think every trailer in every truck shop is unloaded before they bring it
in to repair those burnt out brakes, yet 13 would class that as auto repair,
even if there were 100 trucks and trailers inside. OHII?

I think that if they are limited by space or whatever to one trailer at a
time, the protection you provide for the storage should just be extended
over the installation area.

Not being a PE it is only my opinion, cause I'm not allowed to make that
kind of determination.

(just a little testy this AM)

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to