What's your basis for requiring two backflow prevention devices?  You  
can use the U-loop with the drilled check valve on the antifreeze  
system w/o a BFP but then your backflow protection between the  
sprinkler system and the potable water can no longer be just a double  
check BFP but must be a reduced-pressure type.

Roland

On Jan 21, 2010, at 8:25 AM, Matt Grise wrote:

> You are correct. There needs to be backflow protection between the  
> public/domestic supply and the sprinkler system, and  also between  
> the wet system and the antifreeze loop.
>
> Matt Grisé PE*, LEED AP
> Sales Engineer
> Alliance Fire Protection
> *Licensed in KS & MO
>