we addressed this issue in a Nov and Dec Tech Updates - see below.   
ALso NFPA 25 at teh ROP moved the text out of the Annex about verify  
that it is Glycerin in CPVC systems.  We moved it back at the ROC  
meeting.

Roland

Testing Antifreeze Systems with CPVC to Verify the Solution is Glycerin



In the November 5, 2009 Tech Update, we identified that one could use  
a field test for glycol (such as that provided by the Noble Company)  
to indirectly determine whether the correct compound was in use by  
showing that the wrong compound (ie glycol) is not present. Such a  
step seemed a reasonable approach since we are not aware of any field  
test for glycerin.  In further conversations with Noble, it has been  
decided that such an approach NOT be applied.  Although the test  
strips will reliably identify glycerin manufactured by Noble, it may  
or may not identify that produced by other manufacturers.  It is also  
possible for compounds other than glycerin to trigger a positive  
result.  Thus, with the potential for false positives and false  
negatives, Noble tests strips for glycol is not an answer to our needs.



Keeping in mind that the owner is responsible for their fire  
protection systems, including complying with NFPA 25 where required,  
and that they are hiring inspectors to perform portions of NFPA 25  
(granted it is often the vast majority of it), discussing this issue  
with your client and addressing it contractually is warranted.



On Jan 21, 2010, at 1:31 PM, Forest Wilson wrote:

> I have a question pertaining to antifreeze loops:
> Contractor performs annual inspection and tests antifreeze loop. The
> antifreeze loop does not identify type of antifreeze used, ie glycerin
> or glycol.
> How does contractor determine type of antifreeze used?
> I have asked this question of a distributor and he said there is no  
> way
> to determine in the field. Said a lab test would be required.
> Does anyone have differing views?
>
> Forest Wilson

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to