Bob:

Wasn't the whole Atrium glass issue because the walls around an atrium were
being treated like exposure protection, not as rated assembly compliance?
What I think I heard, and could be wrong, was that SSP/ssu closely spaces
were wetting the glass or wall, similar to exposure protection since there
was never going to be a fire fighter 30'+ in the air in the atrium hosing
down the glass.

As I said I could be Wong.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob Caputo
Sent: Monday, March 08, 2010 2:12 PM
To: [email protected]
Subject: RE: Window sprinklers

Sal,

I am not challenging your knowledge or expertise, and while I agree that
window sprinklers are tested for this specific application, the use of
sprinklers in lieu of rated construction materials is really a building code
issue where the atrium section permits closely spaced sprinklers in lieu of
the rated glass.  It doesn't prescribe a specific sprinkler in terms of a
listing, nor does it prescribe a deluge water curtain... in fact, it doesn't
specify sprinklers on both sides of the glass.  So wouldn't the answer to
Mr. Thomson's original question simply be that it's up to the requirements
of the local AHJ in each case where sprinklers are used in lieu of rated
glass?

Please know I am not looking to argue - just looking to be clear or to
verify that I've misunderstood this code allowance for years.

Best regards,

Bob Caputo, CFPS, CET
657 Cantara Lane, Vista, CA 92081    

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Monday, March 08, 2010 12:06 PM
To: [email protected]
Subject: RE: Window sprinklers

In answering this question, one must first ask if there is fire resistance
rating required to be maintained with this installation.  Only listed window
sprinklers are tested and listed to provide an actual fire resistance rating
for glazing.  This is because these sprinklers are tested in accordance with
the ASTM E119 standard for fire resistance.  If the glazing is located in a
fire rated assembly, like a rated corridor wall, the fire resistance must be
maintained for the opening protective.  Therefore, if sprinklers were to be
used for this purpose in lieu of fire rated glazing, the listed window
sprinklers must be used.  In addition to the testing for the fire rating,
the positioning of the sprinklers relative to the glazing is also test
specific, as this ensures all areas of the are wetted.  This does not apply
to regular spray sprinklers.

Regards,
Salvatore J. Izzo, P.E. SFPE
Manager - Reliable Technical Services
________________________________________
From: [email protected]
[[email protected]] On Behalf Of Robert Thompson
[[email protected]]
Sent: Monday, March 08, 2010 2:10 PM
To: [email protected]
Subject: Window sprinklers

Do you have to use window sprinklers to protect windows or can standard
spray sprinklers be used?


Thank you
 Robert  Thompson

 DAKOTA
FIRE PROTECTION
1710 N. Washington Street
Grand Forks ND 58206-5327
Phone # (701) 772-8820
Fax # (701) 772-7932
Email [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to