There was a comment that SS sprinklers were used to protect "Small" openings. Some of those small openings such as the windows in doors are OK by code up to a specific size, openings larger than that size would require listed protection in a listed assembly.
Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Sal Izzo (TECH- 103) Sent: Monday, March 08, 2010 1:06 PM To: [email protected] Subject: RE: Window sprinklers In answering this question, one must first ask if there is fire resistance rating required to be maintained with this installation. Only listed window sprinklers are tested and listed to provide an actual fire resistance rating for glazing. This is because these sprinklers are tested in accordance with the ASTM E119 standard for fire resistance. If the glazing is located in a fire rated assembly, like a rated corridor wall, the fire resistance must be maintained for the opening protective. Therefore, if sprinklers were to be used for this purpose in lieu of fire rated glazing, the listed window sprinklers must be used. In addition to the testing for the fire rating, the positioning of the sprinklers relative to the glazing is also test specific, as this ensures all areas of the are wetted. This does not apply to regular spray sprinklers. Regards, Salvatore J. Izzo, P.E. SFPE Manager - Reliable Technical Services ________________________________________ From: [email protected] [[email protected]] On Behalf Of Robert Thompson [[email protected]] Sent: Monday, March 08, 2010 2:10 PM To: [email protected] Subject: Window sprinklers Do you have to use window sprinklers to protect windows or can standard spray sprinklers be used? Thank you Robert Thompson DAKOTA FIRE PROTECTION 1710 N. Washington Street Grand Forks ND 58206-5327 Phone # (701) 772-8820 Fax # (701) 772-7932 Email [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)