There was a comment that SS sprinklers were used to protect "Small"
openings. Some of those small openings such as the windows in doors are OK
by code up to a specific size, openings larger than that size would require
listed protection in a listed assembly.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sal Izzo
(TECH- 103)
Sent: Monday, March 08, 2010 1:06 PM
To: [email protected]
Subject: RE: Window sprinklers

In answering this question, one must first ask if there is fire resistance
rating required to be maintained with this installation.  Only listed window
sprinklers are tested and listed to provide an actual fire resistance rating
for glazing.  This is because these sprinklers are tested in accordance with
the ASTM E119 standard for fire resistance.  If the glazing is located in a
fire rated assembly, like a rated corridor wall, the fire resistance must be
maintained for the opening protective.  Therefore, if sprinklers were to be
used for this purpose in lieu of fire rated glazing, the listed window
sprinklers must be used.  In addition to the testing for the fire rating,
the positioning of the sprinklers relative to the glazing is also test
specific, as this ensures all areas of the are wetted.  This does not apply
to regular spray sprinklers.

Regards,
Salvatore J. Izzo, P.E. SFPE
Manager - Reliable Technical Services
________________________________________
From: [email protected]
[[email protected]] On Behalf Of Robert Thompson
[[email protected]]
Sent: Monday, March 08, 2010 2:10 PM
To: [email protected]
Subject: Window sprinklers

Do you have to use window sprinklers to protect windows or can standard
spray sprinklers be used?


Thank you
 Robert  Thompson

 DAKOTA
FIRE PROTECTION
1710 N. Washington Street
Grand Forks ND 58206-5327
Phone # (701) 772-8820
Fax # (701) 772-7932
Email [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to