Logic? Try this.

Shell retail space with 4-12 pitch wood roof. Rough in core and shell
system for OH2 at 10 ft. x 12 ft. spacing. Tenant installs a suspended
ceiling. The attic is now light hazard combustible concealed space that
must comply with 8.6.4.1.4. A lesser hazard yet the OH2 design is
lacking.

It's my understanding the spacing requirements of 8.6.4.1.4 are a result
of full scale testing. If testing proved the spacing works why is a 30%
increase of the RA still required?

Some of the many mysteries in 13.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, March 16, 2010 12:05 PM
To: [email protected]
Subject: Combustible concealed space

NFPA 13, 2007, 8.6.4.1.4

Does it apply only if the space is "concealed"? A 13 building has an
attic
with 12:6 roof slope, which is sprinklered and has to conform to
8.6.4.1.4.
Some areas in this attic has mechanical rooms with exposed roof
structure as
the rest of the attic. Hence my question. I would think it should apply
to
all steep pitched roofs or ceilings. If not, what is the logic? (if
logic
even enters into the question. Ours not to reason why, ours but to do or
die).

Tony 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to