I have always used the rules of 8.6.4.1.4 to apply to any occupancy with this 
type of roof construction because it is a function of the way heat travels in a 
roof with this shape.Whether it is a concealed space or occupied with a retail 
shop,mechanical room,or anything else,the heat is going to travel up the slope 
in much the same way.IMHO.

Lamar Vaughn,SET

  
---- [email protected] wrote: 
> I couldn't see a mechanical room in any location falling under a concealed 
> space ruling even in an attic.  It definitely wouldn't be a light hazard 
> occupancy. Typically I look on concealed spaces as not being able to store or 
> have any actual use, limited access, etc.  A mechanical space can be occupied 
> and can and probably will be used for storage even if it's just filters.  
> 
> 
> Craig L. Prahl, CET   
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> PO Box 491, Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com 
> 
> 
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of A.P.Silva
> Sent: Wednesday, March 17, 2010 3:31 PM
> To: [email protected]
> Subject: RE: Combustible concealed space
> 
> Any other comments?
> 
> Is NFPA 13 2002, 8.6.4.1.4 applicable only if the space is concealed? If so, 
> will a mech. room built in an attic be considered concealed?
> 
> Tony  
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Fletcher, Ron
> Sent: March 16, 2010 1:20 PM
> To: [email protected]
> Subject: RE: Combustible concealed space
> 
> Logic? Try this.
> 
> Shell retail space with 4-12 pitch wood roof. Rough in core and shell system 
> for OH2 at 10 ft. x 12 ft. spacing. Tenant installs a suspended ceiling. The 
> attic is now light hazard combustible concealed space that must comply with 
> 8.6.4.1.4. A lesser hazard yet the OH2 design is lacking.
> 
> It's my understanding the spacing requirements of 8.6.4.1.4 are a result of 
> full scale testing. If testing proved the spacing works why is a 30% increase 
> of the RA still required?
> 
> Some of the many mysteries in 13.
> 
> 
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
> 
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of A.P.Silva
> Sent: Tuesday, March 16, 2010 12:05 PM
> To: [email protected]
> Subject: Combustible concealed space
> 
> NFPA 13, 2007, 8.6.4.1.4
> 
> Does it apply only if the space is "concealed"? A 13 building has an attic 
> with 12:6 roof slope, which is sprinklered and has to conform to 8.6.4.1.4.
> Some areas in this attic has mechanical rooms with exposed roof structure as 
> the rest of the attic. Hence my question. I would think it should apply to 
> all steep pitched roofs or ceilings. If not, what is the logic? (if logic 
> even enters into the question. Ours not to reason why, ours but to do or die).
> 
> Tony 
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to