In other words room design method is outdated and in effect replaced by section 11.1.2. Why would one ever do room design method with this option?
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Monday, March 22, 2010 10:57 To: [email protected] Subject: RE: Room Design vs. Adjacent Hazards It seems to me that you can meet 11.1.2 without meeting room design requirements, as you state no mention of automatic closing doors or rated walls. I believe that what 11.1.2 is stating is that if the heat from a fire in that 600SF room will set off the heads in that room, without heat activating the sprinklers in the adj. area, then what we expect to happen is for the fire to be contained to the room of origin if that room is properly protected. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richardson, R Sent: Monday, March 22, 2010 11:55 AM To: [email protected] Subject: RE: Room Design vs. Adjacent Hazards It does meet 11.1.2 (subject to a massive interpretation as to what constitutes adequate separation), but does not meet room design because the wall is not fire rated, the doors in the wall are not self-closing and they are not including two heads outside the OH area as required by room design. Rich -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Monday, March 22, 2010 10:42 To: [email protected] Subject: RE: Room Design vs. Adjacent Hazards Rich: How does your 600 Sf OH space not meet the requirements of 11.1.2(2)? And still qualify for room design? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Richardson, R Sent: Monday, March 22, 2010 11:33 AM To: [email protected] Subject: Room Design vs. Adjacent Hazards In reference to 2007 NFPA 13 section 11.1.2 Adjacent Hazards, is this considered a stand-alone code section or does one still have to meet all of the room design criteria. The question is relevant to a situation where a small ordinary hazard space is app. 600 sq.ft. adjacent to a light hazard space and they are using 11.1.2. It seems that section 11.1.2. essentially makes the room design irrelevant. Thanks, Rich Richardson Seattle Fire Department _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)
