Any other comments?

Is NFPA 13 2002, 8.6.4.1.4 applicable only if the space is concealed? If so,
will a mech. room built in an attic be considered concealed?

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Fletcher, Ron
Sent: March 16, 2010 1:20 PM
To: [email protected]
Subject: RE: Combustible concealed space

Logic? Try this.

Shell retail space with 4-12 pitch wood roof. Rough in core and shell system
for OH2 at 10 ft. x 12 ft. spacing. Tenant installs a suspended ceiling. The
attic is now light hazard combustible concealed space that must comply with
8.6.4.1.4. A lesser hazard yet the OH2 design is lacking.

It's my understanding the spacing requirements of 8.6.4.1.4 are a result of
full scale testing. If testing proved the spacing works why is a 30%
increase of the RA still required?

Some of the many mysteries in 13.


Ron Fletcher
Aero Automatic
Phoenix, AZ




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, March 16, 2010 12:05 PM
To: [email protected]
Subject: Combustible concealed space

NFPA 13, 2007, 8.6.4.1.4

Does it apply only if the space is "concealed"? A 13 building has an attic
with 12:6 roof slope, which is sprinklered and has to conform to 8.6.4.1.4.
Some areas in this attic has mechanical rooms with exposed roof structure as
the rest of the attic. Hence my question. I would think it should apply to
all steep pitched roofs or ceilings. If not, what is the logic? (if logic
even enters into the question. Ours not to reason why, ours but to do or
die).

Tony 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to