Was this job located in Colorado, you would become one of the 2800 Water
purveyors in our state, just by having multable wells, and the
responsibility to supply potable water. (I wish we could refrain from using
"Domestic" water, a plumbers term, and refer to potable or non-potable water
sources.) Here in the west, you'd better own those water rights before you
even think of drilling a well.

Your situation sounds similar to a Int. Latex plant I worked on long ago.
They used the process water holding tank for their fire sprinkler system
supply, and relied upon the municipal water supply for the fire hyd. And
potable water. (The tank was a 2 million gallon holding tank built to NFPA
20, that was alarmed if the water level dropped below 1.5 M Gal.) Diesel and
Elect fire pumps. Deluge systems at the Butadiene storage and unloading
stations, High density in warehouse and loading docks, and lower density in
reactor areas, because they go BOOM before they burn.

Thom McMahon, SET
Firetech, Inc.
2560 Copper Ridge Dr
P.O. Box 882136
Steamboat Springs, CO 80488
Tel:  970-879-7952
Fax: 970-879-7926


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, April 14, 2010 8:46 AM
To: [email protected]
Subject: RE: Wells as a water source

2007 - NFPA 20, Section 7.2 Water Supply, gives plenty of information
regarding wells as water source.  NFPA 1142 also provides some guidance
while not making recommendations for plants such as this.  So there is
information outside of the NFPA 13 set for this type of supply.  While not
optimum, there are cases where it is the only source.  Where the reliability
may be questioned it would obviously be prudent to specify a storage tank as
the primary source. 

At this stage of the project they have no procedures for anything.  This is
the concept stage where you weed out all the potential problems,
irregularities, and obstacles and then work with the client and local AHJ's
to come to a resolution.  


Craig L. Prahl, CET   
field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to