The 1.2x sqrt(RA) is independent of the sprinkler 
spacing. With irregular branch lines, what I tend 
to do is to make sure that the furthest part of 
the remote area meets that requirement and then 
work my way in, keeping that distance as much as 
possible until the line with fewer sprinklers. 
Remember, the RA does not have to be a perfect 
rectangle. The examples in the book are there to 
describe a concept and not be an absolute.



At 02:41 AM 4/20/2010, you wrote:
>If I am calculating a tree type system using the 
>area/design method, and have several different 
>lengths between sprinklers on a branch line. 
>Would I use the longest length to determine the 
>amount of sprinklers on a branch line. I have 
>always used an average (which I've probably been 
>wrong all these years). 1.2√design 
>area            S S= Distance between sprinklers 
>on branch line 1.2√design area            S S= 
>Distance between sprinklers on branch line 
>George Medina Jr. 
>_______________________________________________ 
>Sprinklerforum mailing list 
>[email protected] 
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum 
>For Technical Assistance, send an email to: 
>[email protected] To Unsubscribe, send 
>an email 
>to:[email protected] (Put 
>the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to