They did just totally revise their sprinkler data sheets at the beginning of 
the year.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Tuesday, April 20, 2010 11:04 AM
To: [email protected]
Subject: RE: Calc Area

I think the FM requirement is changed. For standard applications 1.4 is
required only if the ceiling slope is greater than a certain value. I think
1 to 12 (off the top of my head). For flat ceiling it is 1.2. This is from
the last time I've checked FM requirements. Could be it is changed again.

Tony  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: April 20, 2010 8:59 AM
To: [email protected]; [email protected]
Subject: Re: Calc Area

And remember that FM is 1:1.4 suggesting that the adjusted ratio for each
entity has to be equal to or greater than 1: 1.2 (NFPA) or 1:1.4 (FM).

On Tue, Apr 20, 2010 at 7:54 AM, Brad <[email protected]> wrote:
> Something I overlooked until about 8 years ago: 1.2 x AREA USED--- 
> Example 1500 SF- min. length 46.5', maybe 4 heads---- 1590 SF- min. 
> length 48', maybe 5 heads!
>
> -----Original Message-----
> From: Roland Huggins [mailto:[email protected]]
> Sent: Tuesday, April 20, 2010 9:36 AM
> To: [email protected]
> Subject: Re: Calc Area
>
> counting sprinklers is ONLY a casual means to check to ensure you are 
> CLOSE to the required floor area.  You must measure actual floor area 
> with no regard to sprinkler spacing or distance to wall.  Now in 
> defining the area of coverage for each sprinkler, your question raises 
> a point often asked.  In a non-symmetrical layout, you use the longer 
> on each side to define S and L such that the sprinkler is always in 
> the center of the imaginary box.  Not well explained by the standard 
> since it mainly talks about distance to walls.
>
> Roland
>
>
> On Apr 19, 2010, at 11:41 PM, George Medina Jr wrote:
>
>>
>> If I am calculating a tree type system using the area/design method, 
>> and have several different lengths between sprinklers on a branch 
>> line. Would I use the longest length to determine the amount of 
>> sprinklers on a branch line. I have always used an average (which 
>> I've probably been wrong all these years).
>>
>> 1.2vdesign area
>>           S
>> S= Distance between sprinklers on branch line
>>
>>
>>
>> 1.2vdesign area
>>           S
>> S= Distance between sprinklers on branch line
>>
>>
>>
>>
>> George Medina Jr.
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to