Be leery of NFPA 303, last time I checked that standard still specified a 
largely useless standpipe system for piers.  The standard requires a class III 
standpipe at some length but allows the supply pipe to be sized to class II.  
In other words largely useless for most fire depts..

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Monday, May 03, 2010 14:14
To: [email protected]
Subject: RE: boat storage

Check in NFPA 303 also.  303 has supposedly equated racked boat storage to 
group A plastics storage as referenced in NFPA 13.  

Other options include water mist and Hybrid water based inert gas systems 
(Vortex).  

NFPA 303, 2006
6.3.4 Indoor Rack Storage.
6.3.4.1* Where boats are stored on multilevel racks in buildings,
an approved automatic fire-extinguishing system shall be
installed throughout the building unless otherwise permitted
by 6.3.4.2 or 6.3.4.3.
6.3.4.2 An automatic fire-extinguishing system shall not be
required for buildings less than 5000 ft2 (465 m2) having multilevel
racks where provided with one of the following:
(1) An automatic fire detection and alarm system supervised
by a central station complying with NFPA 72, National Fire
Alarm Code
(2) An automatic fire detection and alarm system supervised
by a local protective signaling system complying with
NFPA 72, National Fire Alarm Code, if the provisions of
6.3.4.2(1) are not technically feasible
(3) A full-time watch service if the provisions of 6.3.4.2(1) are
not technically feasible
6.3.4.3* Existing facilities shall not be required to be protected
by an automatic fire-extinguishing system where acceptable
to the authority having jurisdiction.
6.3.4.4 The design of automatic sprinkler systems shall comply
with the provisions of Chapter 12 of NFPA 13, Standard for
the Installation of Sprinkler Systems, for Group A Plastics stored
on solid shelves.
6.3.5* An approved water supply shall be provided within
100 ft (30 m) of the pier/land intersection or fire department
connection serving fire protection systems.
6.3.6 Access between water supplies and pier/land intersections
or fire department connections shall be by roadway acceptable
to the authority having jurisdiction.

Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of tom poisal
Sent: Monday, May 03, 2010 4:03 PM
To: sprinklerforum
Subject: boat storage

Ii have a in rack boat storage facility, 4 stories, I am thinking that ESFR
16.8 for 12 spkrs however I am not sure what to use as a density, flr to flr
is 20' - 4 racks per floor, just go for the rated flow/psi per head ?
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________