the E.O.R. emphatically states "install a NFPA compliant system"

On 5/3/10, Richardson, R <[email protected]> wrote:
> Be leery of NFPA 303, last time I checked that standard still specified a
> largely useless standpipe system for piers.  The standard requires a class
> III standpipe at some length but allows the supply pipe to be sized to class
> II.  In other words largely useless for most fire depts..
>
> Rich Richardson
> Seattle Fire Department
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of
> [email protected]
> Sent: Monday, May 03, 2010 14:14
> To: [email protected]
> Subject: RE: boat storage
>
> Check in NFPA 303 also.  303 has supposedly equated racked boat storage to
> group A plastics storage as referenced in NFPA 13.
>
> Other options include water mist and Hybrid water based inert gas systems
> (Vortex).
>
> NFPA 303, 2006
> 6.3.4 Indoor Rack Storage.
> 6.3.4.1* Where boats are stored on multilevel racks in buildings,
> an approved automatic fire-extinguishing system shall be
> installed throughout the building unless otherwise permitted
> by 6.3.4.2 or 6.3.4.3.
> 6.3.4.2 An automatic fire-extinguishing system shall not be
> required for buildings less than 5000 ft2 (465 m2) having multilevel
> racks where provided with one of the following:
> (1) An automatic fire detection and alarm system supervised
> by a central station complying with NFPA 72, National Fire
> Alarm Code
> (2) An automatic fire detection and alarm system supervised
> by a local protective signaling system complying with
> NFPA 72, National Fire Alarm Code, if the provisions of
> 6.3.4.2(1) are not technically feasible
> (3) A full-time watch service if the provisions of 6.3.4.2(1) are
> not technically feasible
> 6.3.4.3* Existing facilities shall not be required to be protected
> by an automatic fire-extinguishing system where acceptable
> to the authority having jurisdiction.
> 6.3.4.4 The design of automatic sprinkler systems shall comply
> with the provisions of Chapter 12 of NFPA 13, Standard for
> the Installation of Sprinkler Systems, for Group A Plastics stored
> on solid shelves.
> 6.3.5* An approved water supply shall be provided within
> 100 ft (30 m) of the pier/land intersection or fire department
> connection serving fire protection systems.
> 6.3.6 Access between water supplies and pier/land intersections
> or fire department connections shall be by roadway acceptable
> to the authority having jurisdiction.
>
> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SCĀ  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of tom poisal
> Sent: Monday, May 03, 2010 4:03 PM
> To: sprinklerforum
> Subject: boat storage
>
> Ii have a in rack boat storage facility, 4 stories, I am thinking that ESFR
> 16.8 for 12 spkrs however I am not sure what to use as a density, flr to flr
> is 20' - 4 racks per floor, just go for the rated flow/psi per head ?
> Tom Poisal, CET
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>


-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to