Unless you find ANYTHING in NFPA 13 supporting such an arrangement and  
countering the definition (yes that is a weak place to rely on for not  
doing something but it is quite explicit), I'd go beyond calling it a  
bad idea and say you would be installing a non-conforming system.

Roland

On May 20, 2010, at 8:54 AM, Daniel Merkle wrote:

> I completely agree that it sounds like a bad idea and will do  
> everything that I can to talk the owner out of it. However, I am  
> just trying to figure out if this would even be allowed per code. If  
> the owner persists, I will walk away.
>
> Daniel L. Merkle, CET
> NICET # 118915
> Automatic Sprinkler System Layout, Level III
> "COLONIAL" Fire Protection Systems Inc.
> 937 Linden Ave. W.
> E. Rochester, N.Y. 14445
> Office-(585) 381-7362
> Fax-(585) 381-8263
> E-mail - [email protected]
>
>
>
>
> ________________________________
> From: Todd Williams <[email protected]>
> To: [email protected]
> Sent: Thu, May 20, 2010 11:48:19 AM
> Subject: Re: Ant-Freeze Systems
>
> The definition of anti-freeze systems in NFPA 13
> specifically references it feeding from a wet
> system. Also, is a sprinkler activates, it dump
> anti-freeze, then air and finally water. I don't
> know haw antifreeze would impact water delivery time. Sounds like a  
> bad idea.
>
>
>
> At 11:40 AM 5/20/2010, you wrote:
>> He would like to a line off the dry system to feed the anti-freeze.
>>
>> Daniel L. Merkle, CET
>> NICET # 118915
>> Automatic Sprinkler System Layout, Level III
>> "COLONIAL" Fire Protection Systems Inc.
>> 937 Linden Ave. W.
>> E. Rochester, N.Y. 14445
>> Office-(585) 381-7362
>> Fax-(585) 381-8263
>> E-mail - [email protected]
>>
>>
>>
>>
>> ________________________________
>> From: Matt Grise <[email protected]>
>> To: "[email protected]" <[email protected] 
>> >
>> Sent: Thu, May 20, 2010 11:16:11 AM
>> Subject: RE: Ant-Freeze Systems
>>
>> So he wants to remove the dry pipe valve and
>> replace it with an anti-freeze bfp and expansion
>> tank? Or does he want to take a line off of the
>> dry system to feed the anti-freeze system (keeping the dry system  
>> in place)?
>>
>> Matt Grisé PE*, LEED AP
>> Sales Engineer
>> Alliance Fire Protection
>> *Licensed in KS & MO
>>
>> 913.888.0647 ph
>> 913.888.0618 f
>> 913.927.0222 cell
>> www. AFPsprink.com
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of  
>> Daniel Merkle
>> Sent: Thursday, May 20, 2010 10:05 AM
>> To: [email protected]
>> Subject: Ant-Freeze Systems
>>
>> Based on the 2002 version of NFPA-13 is there
>> anything that restricts an anti-freeze system
>> from being piped off of a dry system? I have an
>> owner of a building with a relatively small
>> attic that has a dry system in place that was
>> not installed properly and he would like to make
>> this portion of his attic an anti-freeze system
>> instead of correcting the pitch of the pipes,
>> etc. Part of the reason for this is that the
>> existing dry system has dry pendents and if the
>> pitch is corrected he would be looking at
>> replacing a lot of them. (BTW this is not my
>> idea. He got this idea from an engineer/friend of his.)
>>
>> Daniel L. Merkle, CET
>> NICET # 118915
>> Automatic Sprinkler System Layout, Level III
>> "COLONIAL" Fire Protection Systems Inc.
>> 937 Linden Ave. W.
>> E. Rochester, N.Y. 14445
>> Office-(585) 381-7362
>> Fax-(585) 381-8263
>> E-mail - [email protected]
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to