For clarification from the 2010 edition, Caps mine:

3.4.1 Antifreeze Sprinkler System. A wet pipe sprinkler system
employing automatic sprinklers that are attached to a piping
system that contains an antifreeze solution and that are connected
to a water supply. The antifreeze solution is discharged,
followed by WATER, immediately upon operation of sprinklers
opened by heat from a fire.

3.4.10 Wet Pipe Sprinkler System. A sprinkler system employing
automatic sprinklers attached to a piping system containing
water and connected to a water supply so that WATER discharges
immediately from sprinklers opened by heat from a fire.

 
R/
Matt
 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]

> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of Roland Huggins
> >Sent: Thursday, May 20, 2010 3:10 PM
> >To: [email protected]
> >Subject: Re: Ant-Freeze Systems
> >
> >Unless you find ANYTHING in NFPA 13 supporting such an arrangement and
> >countering the definition (yes that is a weak place to rely on for not
> >doing something but it is quite explicit), I'd go beyond calling it a
> >bad idea and say you would be installing a non-conforming system.
> >
> >Roland
> >
> >On May 20, 2010, at 8:54 AM, Daniel Merkle wrote:
> >
> >> I completely agree that it sounds like a bad idea and will do
> >> everything that I can to talk the owner out of it. However, I am
> >> just trying to figure out if this would even be allowed per code. If
> >> the owner persists, I will walk away.
> >>
> >> Daniel L. Merkle, CET
> >> NICET # 118915
> >> Automatic Sprinkler System Layout, Level III
> >> "COLONIAL" Fire Protection Systems Inc.
> >> 937 Linden Ave. W.
> >> E. Rochester, N.Y. 14445
> >> Office-(585) 381-7362
> >> Fax-(585) 381-8263
> >> E-mail - [email protected]
> >>
> >>
> >>
> >>
> >> ________________________________
> >> From: Todd Williams <[email protected]>
> >> To: [email protected]
> >> Sent: Thu, May 20, 2010 11:48:19 AM
> >> Subject: Re: Ant-Freeze Systems
> >>
> >> The definition of anti-freeze systems in NFPA 13
> >> specifically references it feeding from a wet
> >> system. Also, is a sprinkler activates, it dump
> >> anti-freeze, then air and finally water. I don't
> >> know haw antifreeze would impact water delivery time. Sounds like a
> >> bad idea.
> >>
> >>
> >>
> >> At 11:40 AM 5/20/2010, you wrote:
> >>> He would like to a line off the dry system to feed the anti-freeze.
> >>>
> >>> Daniel L. Merkle, CET
> >>> NICET # 118915
> >>> Automatic Sprinkler System Layout, Level III
> >>> "COLONIAL" Fire Protection Systems Inc.
> >>> 937 Linden Ave. W.
> >>> E. Rochester, N.Y. 14445
> >>> Office-(585) 381-7362
> >>> Fax-(585) 381-8263
> >>> E-mail - [email protected]
> >>>
> >>>
> >>>
> >>>
> >>> ________________________________
> >>> From: Matt Grise <[email protected]>
> >>> To: "[email protected]"
> ><[email protected]
> >>> >
> >>> Sent: Thu, May 20, 2010 11:16:11 AM
> >>> Subject: RE: Ant-Freeze Systems
> >>>
> >>> So he wants to remove the dry pipe valve and
> >>> replace it with an anti-freeze bfp and expansion
> >>> tank? Or does he want to take a line off of the
> >>> dry system to feed the anti-freeze system (keeping the dry system
> >>> in place)?
> >>>
> >>> Matt Grisé PE*, LEED AP
> >>> Sales Engineer
> >>> Alliance Fire Protection
> >>> *Licensed in KS & MO
> >>>
> >>> 913.888.0647 ph
> >>> 913.888.0618 f
> >>> 913.927.0222 cell
> >>> www. AFPsprink.com
> >>>
> >>>
> >>> -----Original Message-----
> >>> From: [email protected]
> >>> [mailto:[email protected]] On Behalf Of
> >>> Daniel Merkle
> >>> Sent: Thursday, May 20, 2010 10:05 AM
> >>> To: [email protected]
> >>> Subject: Ant-Freeze Systems
> >>>
> >>> Based on the 2002 version of NFPA-13 is there
> >>> anything that restricts an anti-freeze system
> >>> from being piped off of a dry system? I have an
> >>> owner of a building with a relatively small
> >>> attic that has a dry system in place that was
> >>> not installed properly and he would like to make
> >>> this portion of his attic an anti-freeze system
> >>> instead of correcting the pitch of the pipes,
> >>> etc. Part of the reason for this is that the
> >>> existing dry system has dry pendents and if the
> >>> pitch is corrected he would be looking at
> >>> replacing a lot of them. (BTW this is not my
> >>> idea. He got this idea from an engineer/friend of his.)
> >>>
> >>> Daniel L. Merkle, CET
> >>> NICET # 118915
> >>> Automatic Sprinkler System Layout, Level III
> >>> "COLONIAL" Fire Protection Systems Inc.
> >>> 937 Linden Ave. W.
> >>> E. Rochester, N.Y. 14445
> >>> Office-(585) 381-7362
> >>> Fax-(585) 381-8263
> >>> E-mail - [email protected]
> >>>
> >>>
> >>>
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>>
> >>>
> >>>
> >>>
> >>> _______________________________________________
> >>> Sprinklerforum mailing list
> >>> [email protected]
> >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>> For Technical Assistance, send an email to: [email protected]
> >>>
> >>> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >>> (Put the word unsubscribe in the subject field)
> >>
> >> Todd G. Williams, PE
> >> Fire Protection Design/Consulting
> >> Stonington, CT
> >> 860.535.2080
> >> www.fpdc.com
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >>
> >>
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email to:Sprinklerforum-
> >[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.819 / Virus Database: 271.1.1/2883 - Release Date: 05/20/10
> >01:26:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to