Deflector will be about 14". Duct insulation and at least 1" below to 
get it in the fitting.



At 09:25 AM 7/2/2010, you wrote:
>Still on first cup so..
>
>What is the prob with 7'-1"? Can the deflector be installed at 12" (even
>with BOD) either as upright or pend?
>
>  Matt
>
>
>
>Matthew J. Willis, CET
>Automatic Fire Sprinklers
>Norred Fire Systems L.L.C.
>318-387-1134 Voice
>318-816-1087 Mobile
>318-387-1163 Facsimile
>[email protected]
> > >-----Original Message-----
> > >From: [email protected] [mailto:sprinklerforum-
> > >[email protected]] On Behalf Of Todd Williams
> > >Sent: Friday, July 02, 2010 8:15 AM
> > >To: [email protected]
> > >Subject: Ceiling pocket
> > >
> > >I am working on a building with a 9'-3" wide corridor. Along one wall
> > >is a duct 2'-9" wide and 12" deep. The sprinkler piping in this space
> > >will be exposed. My original plan was to run a line along side of the
> > >duct  with sidewalls and put pendent sprinklers under the duct.
> > >(running along the other wall is not an option.) However, the pendent
> > >sprinklers under the duct will be 7'-1" from the far wall. I was
> > >looking to see if I could apply the ceiling pocket  section to this
> > >scenario and eliminate the sidewalls. The total volume of the pocket
> > >is approximately 225 cubic feet. I can't see why this wouldn't apply,
> > >but it seems an odd use of the rule. Thoughts?
> > >
> > >Todd G. Williams, PE
> > >Fire Protection Design/Consulting
> > >Stonington, CT
> > >860.535.2080
> > >www.fpdc.com
> > >
> > >_______________________________________________
> > >Sprinklerforum mailing list
> > >[email protected]
> > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> > >
> > >For Technical Assistance, send an email to: [email protected]
> > >
> > >To Unsubscribe, send an email to:[email protected]
> > >(Put the word unsubscribe in the subject field)
> > >
> > >No virus found in this incoming message.
> > >Checked by AVG - www.avg.com
> > >Version: 9.0.830 / Virus Database: 271.1.1/2968 - Release Date: 07/01/10
> > >13:35:00
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to