Where do you draw the line; precisely my point. If 6'-6" of the ceiling were low and 2'-9" were high, we would not be having this discussion.
However, I do challenge that it does not meet the definition in 3.3.4. It is an architectural ceiling feature. It is a bounded area of ceiling located at a higher elevation (can be bounded by wall, not just more ceiling, no?) and it is attached to a lower ceiling. That is where you might have an argument that the duct is not attached to the upper ceiling. If the duct was boxed in (which they might do), would this then not meet the definition in full? At 10:00 AM 7/2/2010, you wrote: >It doesn't meet the definition provided by 3.3.4, NFPA 13 (10ed) but I >think it meets the intent of the rule. >You would think that since the volume of the high area is within the >limits if what is required to apply the ceiling pocket rule then there >would not be a significant delay in sprinkler operation for the >deflector positioned below the soffit. >But where do you draw the line? Using my Vulcan logic, one could apply >this thinking to any small room with a soffit and I do not think this is >the correct road to follow. >Dewayne > >-----Original Message----- >From: [email protected] >[mailto:[email protected]] On Behalf Of Todd >Williams >Sent: Friday, July 02, 2010 8:32 AM >To: [email protected] >Subject: RE: Ceiling pocket > >Deflector will be about 14". Duct insulation and at least 1" below to >get it in the fitting. > > > >At 09:25 AM 7/2/2010, you wrote: > >Still on first cup so.. > > > >What is the prob with 7'-1"? Can the deflector be installed at 12" >(even > >with BOD) either as upright or pend? > > > > Matt > > > > > > > >Matthew J. Willis, CET > >Automatic Fire Sprinklers > >Norred Fire Systems L.L.C. > >318-387-1134 Voice > >318-816-1087 Mobile > >318-387-1163 Facsimile > >[email protected] > > > >-----Original Message----- > > > >From: [email protected] >[mailto:sprinklerforum- > > > >[email protected]] On Behalf Of Todd Williams > > > >Sent: Friday, July 02, 2010 8:15 AM > > > >To: [email protected] > > > >Subject: Ceiling pocket > > > > > > > >I am working on a building with a 9'-3" wide corridor. Along one >wall > > > >is a duct 2'-9" wide and 12" deep. The sprinkler piping in this >space > > > >will be exposed. My original plan was to run a line along side of >the > > > >duct with sidewalls and put pendent sprinklers under the duct. > > > >(running along the other wall is not an option.) However, the >pendent > > > >sprinklers under the duct will be 7'-1" from the far wall. I was > > > >looking to see if I could apply the ceiling pocket section to this > > > >scenario and eliminate the sidewalls. The total volume of the >pocket > > > >is approximately 225 cubic feet. I can't see why this wouldn't >apply, > > > >but it seems an odd use of the rule. Thoughts? > > > > > > > >Todd G. Williams, PE > > > >Fire Protection Design/Consulting > > > >Stonington, CT > > > >860.535.2080 > > > >www.fpdc.com > > > > > > > >_______________________________________________ > > > >Sprinklerforum mailing list > > > >[email protected] > > > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > > > > > >For Technical Assistance, send an email to: >[email protected] > > > > > > > >To Unsubscribe, send an email >to:[email protected] > > > >(Put the word unsubscribe in the subject field) > > > > > > > >No virus found in this incoming message. > > > >Checked by AVG - www.avg.com > > > >Version: 9.0.830 / Virus Database: 271.1.1/2968 - Release Date: >07/01/10 > > > >13:35:00 > > > >_______________________________________________ > >Sprinklerforum mailing list > >[email protected] > >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > >For Technical Assistance, send an email to: [email protected] > > > >To Unsubscribe, send an email >to:[email protected] > >(Put the word unsubscribe in the subject field) > >Todd G. Williams, PE >Fire Protection Design/Consulting >Stonington, CT >860.535.2080 >www.fpdc.com > >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email >to:[email protected] >(Put the word unsubscribe in the subject field) >_______________________________________________ >Sprinklerforum mailing list >[email protected] >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > >For Technical Assistance, send an email to: [email protected] > >To Unsubscribe, send an email to:[email protected] >(Put the word unsubscribe in the subject field) Todd G. Williams, PE Fire Protection Design/Consulting Stonington, CT 860.535.2080 www.fpdc.com _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)