But if it's a 90 year old system, then they most likely used Cast Iron Tee's
on the mains as well and every section of pipe will trap water.

T

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Friday, August 27, 2010 1:26 PM
To: [email protected]
Subject: RE: dry main low point drains

90 year old system, 250 ft long building. Have to remove about 1/2 of 
branch lines and re-do riser nipples and cut riser to pitch main. 
Messing with an old system can be a recipe for disaster. If you did 
one for every pipe size, this would require 8-10 drum drips, which 
could be made up in the shop and connected to the main with 
mechanical tees. Sounds a whole lot easier and cheaper to me. This 
owner has a good track records maintaining systems.





At 02:17 PM 8/27/2010, you wrote:
>There used to be a "Manifold drain" allowed for very small DP systems with
>like 1" branch lines. I think that now it's called "Tie-in Drains"
>8.16.2.5.3.5 anyway it's still for trapped branch lines. If the drains, One
>for each pipe section of main are not "Too Much Money" why would
>"Re-hanging" the main be too much? I'd rather re-hang 40 pieces of main
than
>pipe 40 drum drips to it and then have to rely on the owner to service them
>"As Required"
>
>T.
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to