Then why doesn't NFPA and/or the Building Codes state that? (i.e not include it in the same section as porte cochere). It would make our lives easier.

A8.15.7.5 describes "Short-term transient storage" and states that it should not be considered storage or handing of combustibles. So if a pallet of goods is put down on a dock while a truck is being loaded and organized for deliveries, would that be short-term transient storage? I think the original question was in effect, what constitutes "short-term"? Legit question. Goes back to my unattended comment.

I know appendix material is not part of the standard, however, it is quite frequently either incorporated into Code or used for interpretation.



At 08:49 AM 8/30/2010, you wrote:
Exactly. That's why you protect it if its intended use is storage. We're not
the police.

A congregation just moved into their new church we sprinklered after 29
years in their "temporary" sanctuary. Nuff said?

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Monday, August 30, 2010 8:37 AM
To: [email protected]
Subject: RE: 2010 handling and storage of combustibles

If a pallet touches the ground, it's storage? Difficult to police in real
life.



At 08:26 AM 8/30/2010, you wrote:
>"..not ever stored.." means they are NEVER placed there for any
>reason ever.   I have had the pleasure of playing semantics with
>those who will say, "they are STAGED, not stored", when I ask for how
>long, well that depends, might be a few hours, might be a few days.  So
>from a personal standpoint, staging, handling, storage are
>all treated as storage.   If there is any chance that any
>combustible commodities will be placed within the area for any length
>of time, it's a potential STORAGE area.
>
>Craig L. Prahl, CET
>Fire Protection Specialist
>Mechanical Department
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>[email protected]
>http://www.ch2m.com
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Greg
>McGahan
>Sent: Saturday, August 28, 2010 10:46 PM
>To: [email protected]
>Subject: 2010 handling and storage of combustibles
>
>   Can someone please look in the 2010 handbook and tell me what the
>intent of 8.15.7.1, 2 and 5 is? According to the way I read it -
>
>.1 states that all overhangs over 4' wide need protection UNLESS .2,.3
>or .4 are met.
>.2 states that protection can be omitted if the overhang is over 4'
>wide and made of Non-comb material
>.5 states that protection is required if the overhang is OVER 2' wide
>and combustible materials are STORED
>
>Therefore, if you have a noncombustible canopy that is over 4'-0" wide
>where combustibles are loaded and unloaded but not stored then
>protection is not required regardless of the size of the overhang?
>
>So now we could have a canopy that covers thousands of square feet and
>yet materials are not ever "stored" under them and protection is not
>required?
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to