You guys have all missed a major issue with using 8.6.2.1.2 in 2002 or 2007.
The small room rule is for SSU and SSP heads ONLY, not residential heads.

So if you're using LFII residential heads in a 256 sqft room, but you're
spaced 10' off two walls, you have to use the 40 GPM figure, not 25.6.

Benjamin Young



On Mon, Nov 1, 2010 at 12:46 PM, Sharon Alves <[email protected]>wrote:

> NFPA 13, 8.6.2.1.2  If it meets the small room criteria - "The protection
> area of coverage for each sprinkler in the small room shall be the area of
> the room divided by the number of sprinklers in each room."
>
>
>
>
>
> SHARON ALVES
>
> Senior Fire Sprinkler Designer
>
>
>
> LP Consulting Engineers, Inc.
>
> Mechanical - Electrical - Plumbing Engineers - Fire Protection
>
> 1075 Creekside Ridge Drive, Suite 175
>
> Roseville, CA 95678
>
> P: 916.771.0778 - F: 916.783.9446
>
> [email protected]
>
>
>
> This email and its attachments are the sole property of LP Consulting
> Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2010.
>  This
> communication with its contents may contain confidential and/or legally
> privileged information. It is solely for the use of the intended
> recipient(s). Unauthorized interception, review, use or disclosure is
> prohibited and may violate applicable laws including the Electronic
> Communications Privacy Act. If you are not the intended recipient, please
> contact the sender and destroy all copies of the communication.  The sender
> and its company do not guarantee that this email or its attachments is free
> of viruses nor does it accept any liability for same
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to