That makes no sense.  How did the committee allow a reference to SSU/P
spacing criteria under residential sprinkler design.  It just makes so
little sense.  I was thinking about it as I was driving home... If this is
truly the intent of the code (to average the spacing of residential heads in
small rooms) the correct (in my opinion) IE, non-confusing way to do this
would be to put the same language in the Chapter 8 section about residential
sprinklers or pull 8.6.2.1.2 back into 8.5 or anything other than
referencing residential design methods from SSU/P spacing rules.

I can't be the only person who thinks that doesn't make a lot of sense, can
I?

I'm also shocked that I never noticed this before.  Believe me, I checked
the 2010 edition, thinking maybe it was a mistake that got rectified, etc.
So I guess part of this is sour grapes too.

Benjamin Young



On Mon, Nov 1, 2010 at 7:31 PM, Roland Huggins
<[email protected]>wrote:

> IT is applicable.  In a 13 system, the residential option is now a hybrid
> where we apply both spray sprinkler criteria (ie small room) and residential
> then apply the most demanding.
>
> Roland
>
>
> On Nov 1, 2010, at 3:35 PM, ParsleyConsulting wrote:
>
>  Ben,
>>
>> I don't know that we've missed that reference to SSU/SSP in 8.6.2.1.2.  I
>> would hope that most of those who'd answered had reviewed the information
>> that generated the question in the first place, which is in 11.3.1.3, item
>> (2).  That clearly suggests that the allowance for the discharge to be
>> calculated the same as it would for a small room is acceptable for
>> residential sprinklers as well.
>> --
>> PARSLEY CONSULTING
>> Ken Wagoner, SET
>> 760.745.6181 voice
>> 760.745.0537 fax
>> [email protected] <mailto:[email protected]>e-mail
>> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
>>
>>
>>
>> On 11/1/2010 1:28 PM, Ben Young wrote:
>>
>>> You guys have all missed a major issue with using 8.6.2.1.2 in 2002 or
>>> 2007.
>>> The small room rule is for SSU and SSP heads ONLY, not residential heads.
>>>
>>> So if you're using LFII residential heads in a 256 sqft room, but you're
>>> spaced 10' off two walls, you have to use the 40 GPM figure, not 25.6.
>>>
>>> Benjamin Young
>>>
>>>
>>>
>>> On Mon, Nov 1, 2010 at 12:46 PM, Sharon Alves<[email protected]
>>> >wrote:
>>>
>>>  NFPA 13, 8.6.2.1.2  If it meets the small room criteria - "The
>>>> protection
>>>> area of coverage for each sprinkler in the small room shall be the area
>>>> of
>>>> the room divided by the number of sprinklers in each room."
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> SHARON ALVES
>>>>
>>>> Senior Fire Sprinkler Designer
>>>>
>>>>
>>>>
>>>> LP Consulting Engineers, Inc.
>>>>
>>>> Mechanical - Electrical - Plumbing Engineers - Fire Protection
>>>>
>>>> 1075 Creekside Ridge Drive, Suite 175
>>>>
>>>> Roseville, CA 95678
>>>>
>>>> P: 916.771.0778 - F: 916.783.9446
>>>>
>>>> [email protected]
>>>>
>>>>
>>>>
>>>> This email and its attachments are the sole property of LP Consulting
>>>> Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2010.
>>>>  This
>>>> communication with its contents may contain confidential and/or legally
>>>> privileged information. It is solely for the use of the intended
>>>> recipient(s). Unauthorized interception, review, use or disclosure is
>>>> prohibited and may violate applicable laws including the Electronic
>>>> Communications Privacy Act. If you are not the intended recipient,
>>>> please
>>>> contact the sender and destroy all copies of the communication.  The
>>>> sender
>>>> and its company do not guarantee that this email or its attachments is
>>>> free
>>>> of viruses nor does it accept any liability for same
>>>>
>>>>
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email
>>>> to:[email protected]<to%[email protected]>
>>>> <to%[email protected]<to%[email protected]>
>>>> >
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>>  _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email
>>> to:[email protected]<to%[email protected]>
>>> (Put the word unsubscribe in the subject field)
>>>
>>>  _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email 
>> to:[email protected]<to%[email protected]>
>> (Put the word unsubscribe in the subject field)
>>
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to