That makes no sense. How did the committee allow a reference to SSU/P spacing criteria under residential sprinkler design. It just makes so little sense. I was thinking about it as I was driving home... If this is truly the intent of the code (to average the spacing of residential heads in small rooms) the correct (in my opinion) IE, non-confusing way to do this would be to put the same language in the Chapter 8 section about residential sprinklers or pull 8.6.2.1.2 back into 8.5 or anything other than referencing residential design methods from SSU/P spacing rules.
I can't be the only person who thinks that doesn't make a lot of sense, can I? I'm also shocked that I never noticed this before. Believe me, I checked the 2010 edition, thinking maybe it was a mistake that got rectified, etc. So I guess part of this is sour grapes too. Benjamin Young On Mon, Nov 1, 2010 at 7:31 PM, Roland Huggins <[email protected]>wrote: > IT is applicable. In a 13 system, the residential option is now a hybrid > where we apply both spray sprinkler criteria (ie small room) and residential > then apply the most demanding. > > Roland > > > On Nov 1, 2010, at 3:35 PM, ParsleyConsulting wrote: > > Ben, >> >> I don't know that we've missed that reference to SSU/SSP in 8.6.2.1.2. I >> would hope that most of those who'd answered had reviewed the information >> that generated the question in the first place, which is in 11.3.1.3, item >> (2). That clearly suggests that the allowance for the discharge to be >> calculated the same as it would for a small room is acceptable for >> residential sprinklers as well. >> -- >> PARSLEY CONSULTING >> Ken Wagoner, SET >> 760.745.6181 voice >> 760.745.0537 fax >> [email protected] <mailto:[email protected]>e-mail >> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website >> >> >> >> On 11/1/2010 1:28 PM, Ben Young wrote: >> >>> You guys have all missed a major issue with using 8.6.2.1.2 in 2002 or >>> 2007. >>> The small room rule is for SSU and SSP heads ONLY, not residential heads. >>> >>> So if you're using LFII residential heads in a 256 sqft room, but you're >>> spaced 10' off two walls, you have to use the 40 GPM figure, not 25.6. >>> >>> Benjamin Young >>> >>> >>> >>> On Mon, Nov 1, 2010 at 12:46 PM, Sharon Alves<[email protected] >>> >wrote: >>> >>> NFPA 13, 8.6.2.1.2 If it meets the small room criteria - "The >>>> protection >>>> area of coverage for each sprinkler in the small room shall be the area >>>> of >>>> the room divided by the number of sprinklers in each room." >>>> >>>> >>>> >>>> >>>> >>>> SHARON ALVES >>>> >>>> Senior Fire Sprinkler Designer >>>> >>>> >>>> >>>> LP Consulting Engineers, Inc. >>>> >>>> Mechanical - Electrical - Plumbing Engineers - Fire Protection >>>> >>>> 1075 Creekside Ridge Drive, Suite 175 >>>> >>>> Roseville, CA 95678 >>>> >>>> P: 916.771.0778 - F: 916.783.9446 >>>> >>>> [email protected] >>>> >>>> >>>> >>>> This email and its attachments are the sole property of LP Consulting >>>> Engineers, Inc. and Copyrighted by LP Consulting Engineers, Inc. 2010. >>>> This >>>> communication with its contents may contain confidential and/or legally >>>> privileged information. It is solely for the use of the intended >>>> recipient(s). Unauthorized interception, review, use or disclosure is >>>> prohibited and may violate applicable laws including the Electronic >>>> Communications Privacy Act. If you are not the intended recipient, >>>> please >>>> contact the sender and destroy all copies of the communication. The >>>> sender >>>> and its company do not guarantee that this email or its attachments is >>>> free >>>> of viruses nor does it accept any liability for same >>>> >>>> >>>> >>>> _______________________________________________ >>>> Sprinklerforum mailing list >>>> [email protected] >>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >>>> >>>> For Technical Assistance, send an email to: [email protected] >>>> >>>> To Unsubscribe, send an email >>>> to:[email protected]<to%[email protected]> >>>> <to%[email protected]<to%[email protected]> >>>> > >>>> (Put the word unsubscribe in the subject field) >>>> >>>> _______________________________________________ >>> Sprinklerforum mailing list >>> [email protected] >>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >>> >>> For Technical Assistance, send an email to: [email protected] >>> >>> To Unsubscribe, send an email >>> to:[email protected]<to%[email protected]> >>> (Put the word unsubscribe in the subject field) >>> >>> _______________________________________________ >> Sprinklerforum mailing list >> [email protected] >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum >> >> For Technical Assistance, send an email to: [email protected] >> >> To Unsubscribe, send an email >> to:[email protected]<to%[email protected]> >> (Put the word unsubscribe in the subject field) >> >> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected]<to%[email protected]> > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)