One thing that can happen is pulling a vacuum on private systems
attached to the main.   I don't recall the exact details, but I think it
was in Standish, MI in about 1994 that a hurry-up pump test was pushed
at a retail center for a Home Depot store in order to get ready for a
soft opening.  In spite of the fact that the water purveyor had not yet
finished an upgrade to the main that would be feeding this property and
its two or three big-box anchors.   So when the pump test went toward or
into overflow condition, sprinklers and regulators an irrigation system
across the street from the subject property imploded and there was some
other damage about which I can't recall details.   

If the water supply from which a pump is taking suction is subject to
fluctuations that could put it below the demand (calculated or however
you arrive at that datum) then either a break tank or low suction
throttling device would be an appropriate accessory.   


Steve Leyton
 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
ParsleyConsulting
Sent: Wednesday, November 17, 2010 12:21 PM
To: [email protected]
Subject: Re: Fire Pump's

Brad,

I'd like to ask about your comment:

"good sense to waive off sprinkler calcs as meaningless."

Can you help me understand what you're referring to here?

I thought the concern was valid.  The FM appeared to be asking a 
legitimate question, such as "what happens if the flow at 150% of rated 
capacity draws my municipal main down below 20 psi?"  The 2010 edition 
of NFPA-20 addressed this in the sections I quoted Brian.  I wasn't 
there for those ROP/ROC meetings, but the new material was voted in 
almost unanimously.

Reading that new language in NFPA-20, it also brought up a point I 
hadn't considered - isn't there a requirement to test the fire pump to 
that 150% capacity?  I thought NFPA-25 called for that in the annual 
flow testing in 8.3.3.1.  If the municipal main can't supply the water 
to meet that 150% figure I'd ask the same questions, I think.  Perhaps a

different way than happened for Brian, but I'd ask.

Are you suggesting that such information is irrelevant?
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website


On 11/17/2010 11:29 AM, Brad Casterline wrote:
> This FM's problem is
> that he/she has the good sense to waive off sprinkler calcs as
meaningless.
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to