Ken,
The highest flow I saw was 1560.2 from "UG" to "TEST". You saw 1875 flowing
somewhere?
***********************************

Ralphy,

 From the material that Brian sent over to me, he did indeed show the 
pump flowing 150% of it's rated capacity back to the municipal supply.

At that point on the supply curve the municipal supply could deliver the 
flow, but it would only be at a pressure of approximately 18.8 psi

The supply curve was 86 psi static, 68 psi residual, at a flow of 920 
gpm.  The pump was rated at 1250 gpm at 75 psi.

And I think you're right, based on the info I read in the '10 edition of 
NFPA-20, as well as the notes in NFPA-25 on annual testing, this 
calculation should be done.

The FM who Brian was dealing with wasn't concerned about the sizing of 
the underground, or for that matter, the demand of the fire sprinkler 
system.  His only concern was - apparently - what pressure is available 
from the supply when the flow is pushed to 150% of the rated capacity?  
Sounds to me like a legitimate question.

PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website


On 11/17/2010 1:12 PM, Ralphy Henderson wrote:
> I've done separate calcs in the past just showing the friction losses
occurring during 150% of rated flow. Shouldn't this be done anyways to
verify that the municipal water pressure isn't getting dangerously low?
>
> I'd just show the fire pump flowing the 150% with nothing else going on
just to verify A) The UG is sized appropriately and B) You're not sucking
the municipal water dry.
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to