Vince said " Now out of curiosity since he's "the Authority", wouldn't
that be reference enough?"  Absolutely not!  Unless there is an adopted
amendment the AHJ cannot legislate his/her ideas from the desk they are
sitting in.

Bob knight

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince
Sabolik
Sent: Thursday, December 09, 2010 8:07 AM
To: [email protected]
Subject: Re: partial egress system

This sounds like a "wet exit" that they used to do in New York.
The idea is that folks could evac a fire along a corridor of disharging
heads.

Now out of curiosity since he's "the Authority", wouldn't that be
reference enough?

 
Vince 


At 07:51 AM 12/9/2010, you wrote:
>I have an AHJ that is requesting a partial system in an existing 8 
>family apartment building (two story). He wants sprinklers by all 
>windows and doors near exterior fire escapes and sprinklers under the 
>platforms of the FE's. There are no sprinklers currently in the 
>building. When I asked him for the Code reference, he said "You're the 
>design professional, you tell me." The CT Fire Safety Code is a 
>bastardized version of the IFC and NFPA 101 and I can't find any 
>reference to it. Anybody out there heard of such a thing?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to