Sorry, not sure where this thread ended but here is a reference to consider:

8.15.3.2.4    Sprinklers shall be permitted to be omitted from exterior stair 
towers when the exterior walls of the stair tower are at least 50 percent open 
and when the stair tower is entirely of noncombustible construction. 


Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


At 07:51 AM 12/9/2010, you wrote:
>I have an AHJ that is requesting a partial system in an existing 8 
>family apartment building (two story). He wants sprinklers by all 
>windows and doors near exterior fire escapes and sprinklers under 
>the platforms of the FE's. There are no sprinklers currently in the 
>building. When I asked him for the Code reference, he said "You're 
>the design professional, you tell me." The CT Fire Safety Code is a 
>bastardized version of the IFC and NFPA 101 and I can't find any 
>reference to it. Anybody out there heard of such a thing?
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Vince Sabolik
Christi Fire Protection, Inc.
11351 Pearl Road
Strongsville, Ohio 44136

T 440 572-7730  F 440 572-7719  Email: 
<mailto:[email protected]>[email protected]

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to