Yes.

2008 NFPA-70 (NEC) 110.26(F) 

(F) Dedicated Equipment Space. All switchboards, panelboards, distribution
boards, and motor control centers shall be located in dedicated spaces and
protected from damage.

(1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through
(F)(1)(d).

(a) Dedicated Electrical Space. The space equal to the width and depth of
the equipment and extending from the floor to a height of 1.8 m (6 ft) above
the equipment or to the structural ceiling, whichever is lower, shall be
dedicated to the electrical installation. No piping, ducts, leak protection
apparatus, or other equipment foreign to the electrical installation shall
be located in this zone.

Exception: Suspended ceilings with removable panels shall be permitted
within the 1.8-m (6-ft) zone.

(b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by
110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided
PROTECTION IS INSTALLED to avoid damage to the electrical equipment from
condensation, LEAKS, OR BREAKS IN SUCH FOREIGN SYSTEMS.

(c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the
dedicated space where the piping complies with this section.

(d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does
not add strength to the building structure shall not be considered a
structural ceiling.


In other words the dedicated equipment space is a three dimensional
exclusion zone above and around switchboards, panelboards, distribution
boards, and motor control centers which is reserved for electrical wiring
only. The space begins at the floor, the width and depth of the equipment
and to a height of 6ft above the equipment or to the STRUCTURAL ceiling
whichever is LOWER. So keep out unless you're the electrician.

Take heed of (C), the operative term is PROTECTION not PIPING. So you can
spray water in the dedicated space, just don't run the pipe in there.

Hope this helps,


John Drucker, CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jay White
Sent: Tuesday, March 01, 2011 5:23 PM
To: [email protected]
Subject: Electrical Rooms

Wet system piping running thru electrical panel rooms, NFPA does allow this,
correct? I guess I'm second guessing myself.

Jay White
Estimator/Design Manager
Dynamic Fire Protection
1807 Hwy. 25 South
Starkville, MS 39759
Phone: 662-324-1550
Fax:       662-324-1545
Cell:      662-312-2426


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to