Elevator machine rooms can only have sprinkler pipe feeding sprinklers for that room only. Pipes that are foreign to that room like FDC or main drain lines are not allowed.
Joe Burtell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Ed.Tambini Sent: Tuesday, March 01, 2011 3:49 PM To: '[email protected]' Subject: RE: Electrical Rooms Is it allowed for a sprinkler pipe (with sprinklers) to enter one end of the electrical room and continue through and exit to another non-electrical room? Pipe is not passing over any equipment. Are the any special rules that set elevator machine rooms apart from normal electrical rooms? Thanks, Ed Aero -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of John Drucker Sent: Tuesday, March 01, 2011 3:41 PM To: [email protected] Subject: RE: Electrical Rooms Yes. 2008 NFPA-70 (NEC) 110.26(F) (F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage. (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d). (a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone. Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone. (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided PROTECTION IS INSTALLED to avoid damage to the electrical equipment from condensation, LEAKS, OR BREAKS IN SUCH FOREIGN SYSTEMS. (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the dedicated space where the piping complies with this section. (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling. In other words the dedicated equipment space is a three dimensional exclusion zone above and around switchboards, panelboards, distribution boards, and motor control centers which is reserved for electrical wiring only. The space begins at the floor, the width and depth of the equipment and to a height of 6ft above the equipment or to the STRUCTURAL ceiling whichever is LOWER. So keep out unless you're the electrician. Take heed of (C), the operative term is PROTECTION not PIPING. So you can spray water in the dedicated space, just don't run the pipe in there. Hope this helps, John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Fire Marshals Office Borough of Red Bank, NJ Not the official position of any agency, association, committee or otherwise. Obtain required applications, permits, inspections and approvals from Authority(s) Having Jurisdiction. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Jay White Sent: Tuesday, March 01, 2011 5:23 PM To: [email protected] Subject: Electrical Rooms Wet system piping running thru electrical panel rooms, NFPA does allow this, correct? I guess I'm second guessing myself. Jay White Estimator/Design Manager Dynamic Fire Protection 1807 Hwy. 25 South Starkville, MS 39759 Phone: 662-324-1550 Fax: 662-324-1545 Cell: 662-312-2426 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)