- rather than (if it worked) a prostrate issue

S
On 28 Jan 2011, at 17:03, rahe.lof...@gsa.gov wrote:

> Sounds like a prostate issue.
> 
> Thank You
> 
> Rahe Loftin, P.E.
> Region 7 - GSA
> Cell - 817-371-3102
> 
> 
> 
> 
> 
>            "Matthew J.                                                   
>            Willis"                                                    To 
>            <matt@norredfire.         <sprinklerforum@firesprinkler.org>  
>            com>                                                       cc 
>            Sent by:                                                      
>            sprinklerforum-bo                                     Subject 
>            unces@firesprinkl         RE: Electrical Rooms                
>            er.org                                                        
> 
> 
>            01/28/2011 07:54                                              
>            AM                                                            
> 
> 
>            Please respond to                                             
>            sprinklerforum@fi                                             
>             resprinkler.org                                              
> 
> 
> 
> 
> 
> 
> The Mythbusters did just that. One episode about the 3rd rail and
> urination,
> the other about a water based taser. In both, they could not get a
> continuous stream, therefore there was no conduction.
> 
> R/
> Matt
> 
> 
> 
> 
> 
> Matthew J. Willis, CET
> Automatic Fire Sprinklers
> Norred Fire Systems L.L.C.
> 318-387-1134 Voice
> 318-816-1087 Mobile
> 318-387-1163 Facsimile
> m...@norredfire.com
>>> -----Original Message-----
>>> From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
>>> boun...@firesprinkler.org] On Behalf Of Stewart Kidd
>>> Sent: Thursday, January 27, 2011 4:59 PM
>>> To: sprinklerforum@firesprinkler.org
>>> Subject: Re: Electrical Rooms
>>> 
>>> I'm with Craig - having spent 10 years managing fire protection for two
>>> electrical utility operations in my sordid youth, this is a subject dear
>>> to my heart.
>>> 
>>> Despite trying for 25 years I've not been able to find any evidence of
>>> anyone having been injured or killed by the conductivity of water being
>>> discharged through a fire suppression system. The origins of the 'risk'
>>> appear to be in research work done by the Sapeurs-Pompiers de Paris in
>>> the late 20's using an experimental rig consisting of two insulated
> metal
>>> branchpipes with a ammeter bridging them.  When a current was passed
>>> through one pipe while they were discharging, the two jets mixed at some
>>> distance from the tips and a current was seen to flow.
>>> 
>>> In real life zip !
>>> 
>>> I wish someone with more money than me would would do a proper
> scientific
>>> study and dispel what is essentially a myth - in the UK this causes us
> to
>>> have install multiple fire extinguishers wherever there is an electrical
>>> risk despite the fact that I routinely specify waterspray on 400 kV
>>> transformers and 25kV turboalternators.
>>> 
>>> Regards
>>> 
>>> Stewart
>>> On 27 Jan 2011, at 20:10, Bobby McCullough wrote:
>>> 
>>>> Maybe scroll through this from January 2010?
>>>> 
>>>> You're correct Ron.  Biggest reasons for not sprinklering is either
>>> fear of accidental head discharge and/or electrocution from the
>>> accidental head discharge.  Neither can be substantiated through
>>> verifiable statistics.
>>>> 
>>>> Last year I did some investigation of reported Industrial accidents
>>> related to electrocutions and the only fire fighter electrocution
>>> recorded for the past 15+ years was for a wildfire where a power line
>>> fell into an area where firefighters were using a hose attack.  There
> was
>>> not one recorded incident of ANY personnel being injured due to water in
>>> an electrical room.
>>>> 
>>>> The perception is that sprinklers randomly discharge all the time, all
>>> sprinkler systems are deluge systems, if someone is standing in the room
>>> when the sprinklers discharge they could be electrocuted.
>>>> 
>>>> Typically dry equipment isn't as great a risk as oil filled, but still
>>> a risk.
>>>> 
>>>> We had a carpet warehouse locally that had a fire begin in their
> second
>>> floor electrical room.  Fortunately it was sprinklered.  The fire was
> out
>>> before the FD arrived.  This place stored millions of dollars of
> imported
>>> rugs.  When the news report stated the sprinkler saved the building, it
>>> was like "YES, Score one for the sprinklers."  They reopened the store
>>> later that day.
>>>> 
>>>> 
>>>> Craig L. Prahl, CET
>>>> Fire Protection Specialist
>>>> Mechanical Department
>>>> CH2MHILL
>>>> Lockwood Greene
>>>> 1500 International Drive
>>>> PO Box 491, Spartanburg, SC  29304-0491
>>>> Direct - 864.599.4102
>>>> Fax - 864.599.8439
>>>> craig.pr...@ch2m.com
>>>> http://www.ch2m.com
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
>>> boun...@firesprinkler.org] On Behalf Of Ron Greenman
>>>> Sent: Tuesday, January 05, 2010 10:39 AM
>>>> To: sprinklerforum@firesprinkler.org
>>>> Subject: Re: Electrical Rooms
>>>> 
>>>> Addressing Craig's mention of perceptions. There is a horrendous fear
>>> of water damage among most (and especially electrical) engineers. I once
>>> had an electrical engineer tell me you couldn't sprinkler a hydro-
>>> electric plant. First because it was too full of electrical equipment
> and
>>> secondly (and more humorously) because there wasn't enough water. When I
>>> pointed out that he had the second biggest river in North America backed
>>> up against one side of his building he told me that you couldn't use
> that
>>> water. I tried to find one of those tables like in 13D as to where fires
>>> most commonly start in commercial buildings but ran out of time. My gut
>>> tells me electrical rooms could be a prime location and electrical
> vaults
>>> (where the transformers are) also seem to be culprits. I just don't have
>>> any numbers to back up MY perceptions so will not try to enforce them.
>>>> 
>>>> On Tue, Jan 5, 2010 at 7:26 AM,  <craig.pr...@ch2m.com> wrote:
>>>>> It makes no difference whether the line passes through the room or
>>> comes in and stops as long as you are in the allowable space as defined
>>> within the section of the electrical code.  People are extrapolating
>>> limitations based on their perception not on code verbiage.  We've had
>>> several detailed discussions on this matter.
>>>>> 
>>>>> 
>>>>> Craig L. Prahl, CET
>>>>> Fire Protection Specialist
>>>>> Mechanical Department
>>>>> CH2MHILL
>>>>> Lockwood Greene
>>>>> 1500 International Drive
>>>>> PO Box 491, Spartanburg, SC  29304-0491 Direct - 864.599.4102 Fax -
>>>>> 864.599.8439 craig.pr...@ch2m.com http://www.ch2m.com
>>>>> 
>>>>> 
>>>>> -----Original Message-----
>>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of
>>>>> cowprop...@aol.com
>>>>> Sent: Tuesday, January 05, 2010 9:44 AM
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Subject: Re: Electrical Rooms
>>>>> 
>>>>> In the handbook of NFPA 72 they show a figure where the sprinkler
> pipe
>>> ends in the electrical room , but it does not go thru the room.
>>>>> mario berrios
>>>>> 
>>>>> 
>>>>> -----Original Message-----
>>>>> From: George Church <for...@ptd.net>
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Sent: Mon, Jan 4, 2010 11:54 am
>>>>> Subject: RE: Electrical Rooms
>>>>> 
>>>>> 
>>>>> Remember they're the ones finding the invisible fault with you
>>>>> crossing an electrical room with your piping.
>>>>> 
>>>>> So that you are sure you comply FULLY with the applicable code
>>>>> preventing you from doing this (ITHO) ask them to provide the
>>>>> applicable code reference.
>>>>> 
>>>>> glc
>>>>> 
>>>>> -----Original Message-----
>>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eladio
>>> N.
>>>>> Alvarado
>>>>> Sent: Monday, January 04, 2010 11:38 AM
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Subject: RE: Electrical Rooms
>>>>> 
>>>>> Eric:
>>>>> 
>>>>> I understand and agree with you, but the EOR insist that the 4" main
>>>>> to the FD Connection, which by the way is dry (check valve in another
>>>>> space) should not cross the room since is in violation of NEC,
>>>>> according to their interpretation. I have already recited chapter and
>>>>> verse of the code requirements and exceptions, but it doesn't seem to
>>>>> sink in. There may other issues that affect their perception or
>>>>> attitude, but I'm kind stuck, and would really like to find
>>>>> irrefutable proof to my point.
>>>>> 
>>>>> Eladio Alvarado
>>>>> AFSDII
>>>>> 
>>>>> -----Original Message-----
>>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>>> [mailto:sprinklerforum-boun...@firesprinkler.org]On Behalf Of Eric
>>>>> Tysinger
>>>>> Sent: Monday, January 04, 2010 10:37 AM
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Subject: RE: Electrical Rooms
>>>>> 
>>>>> To my knowledge, there is nothing from NFPA 13 that addresses this.
>>>>> The clearance requirements are found in the NEC, and there is nothing
>>>>> in the NEC that prohibits piping from entering and exiting the
>>>>> electrical room.
>>>>> Don't
>>>>> forget there are rules in NFPA 13 that allow the sprinkler to be
>>>>> omitted. I try to use these to avoid the questions all together.
>>>>> 
>>>>> Thanks,
>>>>> Eric Tysinger CET
>>>>> NICET 108988
>>>>> Designer
>>>>> Wayne Automatic Fire Sprinklers, Inc.
>>>>> 4370 Motorsport Drive
>>>>> Concord, NC 28027
>>>>> p: (704)782-3032
>>>>> f: (704)795-6838
>>>>> C: (239)633-9703
>>>>> 
>>>>> 
>>>>> -----Original Message-----
>>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eladio
>>> N.
>>>>> Alvarado
>>>>> Sent: Monday, January 04, 2010 9:31 AM
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Subject: Electrical Rooms
>>>>> 
>>>>> Happy New Year to all!!
>>>>> 
>>>>> I know that we have previously discussed Electrical Equipment rooms,
>>>>> and that the general consensus is that there is nothing in NFPA 13
>>>>> that prohibits sprinkler pipe, be it mains and/or branch lines from
>>>>> entering the room, as long as it doesn't violate the require
> perimeter
>>>>> area of the particular equipment. Now my question is; is there a
>>>>> technical interpretation from NFPA 13 that explains this, and that
>>>>> someone in the forum may be aware of? I could really use this info to
>>>>> nail this subject closed with the EOR.
>>>>> 
>>>>> Thanks in advanced,
>>>>> 
>>>>> Eladio Alvarado
>>>>> AFSDII
>>>> 
>>>> -----Original Message-----
>>>> From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-
>>> boun...@firesprinkler.org] On Behalf Of Brian Harris
>>>> Sent: Thursday, January 27, 2011 2:59 PM
>>>> To: sprinklerforum@firesprinkler.org
>>>> Subject: RE: Electrical Rooms
>>>> 
>>>> C'mon man!
>>>> 
>>>> Brian Harris
>>>> FDFP Inc.
>>>> 
>>>> 
>>>> -----Original Message-----
>>>> From: sprinklerforum-boun...@firesprinkler.org
>>>> [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Mike
>>>> Hairfield
>>>> Sent: Thursday, January 27, 2011 2:54 PM
>>>> To: AFSA SprinklerFORUM
>>>> Subject: RE: Electrical Rooms
>>>> 
>>>> 
>>>> This is Lazy, look it up in the NEC
>>>> 
>>>>> From: br...@firstdefensefire.com
>>>>> To: sprinklerforum@firesprinkler.org
>>>>> Subject: Electrical Rooms
>>>>> Date: Thu, 27 Jan 2011 14:47:30 -0500
>>>>> 
>>>>> I'm being lazy but does anybody know off the top of their head if you
>>> can
>>>>> run sprinkler lines over an Electrical room if it has a ceiling?
>>>>> 
>>>>> 
>>>>> 
>>>>> Thanks!
>>>>> 
>>>>> 
>>>>> 
>>>>> Brian Harris
>>>>> 
>>>>> First Defense Fire Protection
>>>>> 
>>>>> 11957 Ramah Church Road
>>>>> 
>>>>> Huntersville, NC 28078
>>>>> 
>>>>> Phone: 704.948.3506
>>>>> 
>>>>> Fax: 704.948.3507
>>>>> 
>>>>> Nicet # 128476
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> 
>>>>> =======
>>>>> Email scanned by PC Tools - No viruses or spyware found.
>>>>> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
>>>>> http://www.pctools.com/
>>>>> =======
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> Sprinklerforum@firesprinkler.org
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>> 
>>>>> For Technical Assistance, send an email to: supp...@firesprinkler.org
>>>>> 
>>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>> requ...@firesprinkler.org
>>>>> (Put the word unsubscribe in the subject field)
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@firesprinkler.org
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> For Technical Assistance, send an email to: supp...@firesprinkler.org
>>>> 
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>> requ...@firesprinkler.org
>>>> (Put the word unsubscribe in the subject field)
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> =======
>>>> Email scanned by PC Tools - No viruses or spyware found.
>>>> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
>>>> http://www.pctools.com/
>>>> =======
>>>> 
>>>> 
>>>> 
>>>> 
>>>> 
>>>> =======
>>>> Email scanned by PC Tools - No viruses or spyware found.
>>>> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
>>>> http://www.pctools.com/
>>>> =======
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@firesprinkler.org
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> For Technical Assistance, send an email to: supp...@firesprinkler.org
>>>> 
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>> requ...@firesprinkler.org
>>>> (Put the word unsubscribe in the subject field)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> Sprinklerforum@firesprinkler.org
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> For Technical Assistance, send an email to: supp...@firesprinkler.org
>>>> 
>>>> To Unsubscribe, send an email to:Sprinklerforum-
>>> requ...@firesprinkler.org
>>>> (Put the word unsubscribe in the subject field)
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> Sprinklerforum@firesprinkler.org
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> 
>>> For Technical Assistance, send an email to: supp...@firesprinkler.org
>>> 
>>> To Unsubscribe, send an email
> to:sprinklerforum-requ...@firesprinkler.org
>>> (Put the word unsubscribe in the subject field)
>>> No virus found in this incoming message.
>>> Checked by AVG - www.avg.com
>>> Version: 9.0.872 / Virus Database: 271.1.1/3404 - Release Date: 01/27/11
>>> 01:37:00
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: supp...@firesprinkler.org
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)
> 
> 
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@firesprinkler.org
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: supp...@firesprinkler.org
> 
> To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to