Let's hope Steve doesn't see Ed McMahon anytime soon!

Mike Brown
Project Designer
Sunland Fire Protection, Inc. 
1218 Elon Place 
High Point, NC 27263
[email protected]   
Business:  336-886-7027 Ext. #140
Fax:  336-886-7024
   

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Monday, March 14, 2011 12:41 AM
To: [email protected]; [email protected]
Subject: Re: Sprinkler under first accessible landing

I should have known. Your kudos are on the way. Watch for Ed McMahon
in a white van carrying large, novelty kudos.

On Sun, Mar 13, 2011 at 9:11 PM, steve <[email protected]> wrote:
> That was me; send all kudos to my office address please.  Collections lagging 
> badly.
>
>
> Sent from my Verizon Wireless BlackBerry
>
> -----Original Message-----
> From: Ron Greenman <[email protected]>
> Sender: [email protected]
> Date: Sun, 13 Mar 2011 19:39:50
> To: <[email protected]>
> Reply-To: [email protected]
> Subject: Re: Sprinkler under first accessible landing
>
> Craig,
>
> I thought it was you making fun of the architect by pointing out his
> misinterpretation was as silly as defining accessibility in this case
> as being the ADA one. I know someone mentioned it. I apologize for the
> attribution but it was praise for the satirical observation. So
> whoever it was: Kudos.
>
> On Sun, Mar 13, 2011 at 6:52 PM,  <[email protected]> wrote:
>> I didn't mention anything related to ADA and it's referencve to 
>> "accessibility".  A stair landing has nothing to do with ADA, that would be 
>> totally stupid.
>>
>> Hans,  sorry but if the PE read the handbook which gives an explanation he 
>> would have understood the reason for the head under the FIRST landing, not 
>> just ANY landing that you can access.  The two common places where storage 
>> occurs are under the FIRST landing on ground level and on the extra width 
>> that isn't used at the TOP of the stairs.  Some of this stuff is just too 
>> simple but some who live to revel in the excellance of their superior 
>> education like to make it more difficult.  So my Star detraction still 
>> stands.  Sorry, just can't excuse blantant ignorance.
>>
>>
>> Craig Prahl
>> CH2MHILL/SPB
>> 864-599-4102
>>________________________________________
>> From: [email protected] 
>> [[email protected]] On Behalf Of Ron Greenman 
>> [[email protected]]
>> Sent: Sunday, March 13, 2011 12:28 PM
>> To: [email protected]
>> Subject: Re: Sprinkler under first accessible landing
>>
>> Problem is that the term is not defined per 13 and so do you use
>> Webster, IBC or ADA? Although a non-building person would probably
>> default to a Websteristic definition and just ask, "Can you get into
>> and use the space for something?" but a building guy will more likely
>> fall into accessible/non-accessible concealed space (which isn't even
>> in 13 in those words), or accessible through an access panel, or, per
>> Craig's comment/joke, do you use ADA and build a ramp to above the
>> ATC. Considering some of the costly insanity associated with ADA
>> interpretation there may be more truth to what Craig said than he was
>> thinking when he said it. Take Texas with horn/strobes in closets in
>> case a  deaf person is in the closet. What if it's a blind and deaf
>> person? Or in my own case. My classrooms are in the semi basement
>> (side of hill, full-flight of stairs to floor above for one egress and
>> half-flight up on the downslope side. There's also a non-compliant
>> ramp that's too steep for ADA. I also have two sinks with soap and
>> towel dispensers. One day maintenance shows up and announces that per
>> ADA they have to lower all the dispensers to some ADA height standard
>> for wheelchair accessibility. Now the sinks stay the same but the
>> towels and soap dispensers are essentially on the floor. Although I
>> could potentially have a wheelchair bound student I never have (or
>> maybe I have but he died on the ramp on his first day when he lost
>> control of his chair), but I have had numerous re-trains that have
>> hurt their backs and have trouble or even pain bending over. These
>> devices WERE non-accessible to them. Were comes into the equation
>> since I have tools and I'm not afraid to use them.
>>
>> On Sun, Mar 13, 2011 at 8:44 AM, Frans Stoop <[email protected]> wrote:
>>> Craig,
>>>
>>> Don't be to greedy with the gold stars to that poor engineer or one day you
>>> might have to hand over one of your own.
>>> The engineer did not take any license, he only quoted the most recent
>>> edition of NFPA 13.
>>> The word "accessible" might not be in the 2007 edition, but it does show up
>>> in the 2010 edition:
>>>
>>> "8.15.3.2.1 In noncombustible stair shafts having noncombustible
>>> stairs with noncombustible or limited-combustible finishes, sprinklers shall
>>> be installed at the top of the shaft and under the first accessible landing
>>> above the bottom of the shaft."
>>>
>>> In fact the word "accessible" is the only difference in the wording of this
>>> paragraph between the two editions.
>>>
>>> Met vriendelijke groet / Yours sincerely,
>>>
>>> Frans Stoop
>>> TOS architecture & fire protection
>>> Netherlands <[email protected]>
>>> Tel. +31-24-324 0112
>>>
>>>
>>> At 06:39 11-3-2011 -0700, you wrote:
>>>>
>>>> Under the lowest landing due to the possibility of that space being used
>>>> for storage.  If the space is totally enclosed then there is no access for
>>>> storage and no head is required if the stair is non-combustible.  The spec
>>>> is correct.  <sigh> The Engineer has taken some license on his quote of the
>>>> 13 section.  The word "accessible" is not in the script.  So no gold star
>>>> for him.
>>>>
>>>> NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having
>>>> noncombustible stairs with noncombustible or limited combustible finishes,
>>>> sprinklers shall be installed at the top of the shaft and under the first
>>>> landing above the bottom of the shaft."
>>>>
>>>> Craig L. Prahl, CET
>>>> Fire Protection
>>>> CH2MHILL
>>>> Lockwood Greene
>>>> 1500 International Drive
>>>> Spartanburg, SC  29304-0491
>>>> Direct - 864.599.4102
>>>> Fax - 864.599.8439
>>>> CH2MHILL Extension  74102
>>>> [email protected]
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: [email protected]
>>>> [mailto:[email protected]] On Behalf Of Cory Power
>>>> Sent: Friday, March 11, 2011 7:19 AM
>>>> To: [email protected]
>>>> Subject: Sprinkler under first accessible landing
>>>>
>>>> I have an an engineer asking to provide a sprinkler under the first
>>>> landing of a non-combustible stairwell. The spec for the job states that
>>>> "Sprinkler shall be installed at top of shaft. Space below first landing
>>>> is considered concealed, non-accessible, non-combustible, and hence does
>>>> not require sprinkler protection."
>>>>
>>>> he engineer who is reviewing my plans sent me an email stating the
>>>> following:
>>>>
>>>> *8.15.3.2 Noncombustible Construction.*
>>>>
>>>> *8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs
>>>> with noncombustible or limited-combustible finishes, sprinklers shall be
>>>> installed at the top of the shaft and under the first
>>>> accessible*landing*above the bottom of the shaft.
>>>>
>>>> We always took this to mean the sprinklers are required under the first
>>>> landing? And by accessible we took this to mean access could be provided
>>>> by a access panel.."
>>>>
>>>> Is this the way I should be interpreting the code? Do I still have to
>>>> sprinkler under the landing and make sure there's an access hatch? or
>>>> should I be able to omit it like the spec indicates?
>>>>
>>>> I have been following this forum for a while now. This is the first
>>>> question I have posted.
>>>>
>>>> - Cory
>>>
>>>_______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>>
>> [email protected]
>>
>> http://www.bates.ctc.edu/fireprotection/
>>
>> 253.680.7346
>> 253.576.9700 (cell)
>>
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>>
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>_______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>_______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to