And here's the simplified text from the 2010 commentary which says the same 
thing as the 2007 commentary.  

NFPA 13, 2010 -*The storage of materials in stairwells obstructs the egress 
route and is prohibited by NFPA
101. However, if there is an open space under the first landing or a large 
landing at the top of
the stairs it is often an irresistible location for transient storage. As a 
result, 8.15.3.2.1 requires
sprinklers at these locations."

OK so let's find a new topic for this week.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Frans Stoop
Sent: Sunday, March 13, 2011 11:45 AM
To: [email protected]
Subject: RE: Sprinkler under first accessible landing

Craig,

Don't be to greedy with the gold stars to that poor engineer or one 
day you might have to hand over one of your own.
The engineer did not take any license, he only quoted the most recent 
edition of NFPA 13.
The word "accessible" might not be in the 2007 edition, but it does 
show up in the 2010 edition:

"8.15.3.2.1 In noncombustible stair shafts having noncombustible
stairs with noncombustible or limited-combustible finishes, 
sprinklers shall be installed at the top of the shaft and under the 
first accessible landing above the bottom of the shaft."

In fact the word "accessible" is the only difference in the wording 
of this paragraph between the two editions.

Met vriendelijke groet / Yours sincerely,

Frans Stoop
TOS architecture & fire protection
Netherlands <[email protected]>
Tel. +31-24-324 0112


At 06:39 11-3-2011 -0700, you wrote:
>Under the lowest landing due to the possibility of that space being 
>used for storage.  If the space is totally enclosed then there is no 
>access for storage and no head is required if the stair is 
>non-combustible.  The spec is correct.  <sigh> The Engineer has 
>taken some license on his quote of the 13 section.  The word 
>"accessible" is not in the script.  So no gold star for him.
>
>NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
>noncombustible stairs with noncombustible or limited combustible 
>finishes, sprinklers shall be installed at the top of the shaft and 
>under the first landing above the bottom of the shaft."
>
>Craig L. Prahl, CET
>Fire Protection
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>CH2MHILL Extension  74102
>[email protected]
>
>
>-----Original Message-----
>From: [email protected] 
>[mailto:[email protected]] On Behalf Of Cory Power
>Sent: Friday, March 11, 2011 7:19 AM
>To: [email protected]
>Subject: Sprinkler under first accessible landing
>
>I have an an engineer asking to provide a sprinkler under the first
>landing of a non-combustible stairwell. The spec for the job states that
>"Sprinkler shall be installed at top of shaft. Space below first landing
>is considered concealed, non-accessible, non-combustible, and hence does
>not require sprinkler protection."
>
>he engineer who is reviewing my plans sent me an email stating the
>following:
>
>*8.15.3.2 Noncombustible Construction.*
>
>*8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs
>with noncombustible or limited-combustible finishes, sprinklers shall be
>installed at the top of the shaft and under the first
>accessible*landing*above the bottom of the shaft.
>
>We always took this to mean the sprinklers are required under the first
>landing? And by accessible we took this to mean access could be provided
>by a access panel.."
>
>Is this the way I should be interpreting the code? Do I still have to
>sprinkler under the landing and make sure there's an access hatch? or
>should I be able to omit it like the spec indicates?
>
>I have been following this forum for a while now. This is the first
>question I have posted.
>
>- Cory

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to