Let's think about this for a moment. We have all basically agreed that
heat collectors do not work. There we are mostly thinking about the 1' x
1' or 18" x 18" variety. However, I think we could all pretty much agree
that if the heat collector was 100' x 100' and the sprinkler was in the
middle, then it would probably activate. So that means that the
effectiveness of any heat collection device is one of scale and design.
We are looking at clouds, as well as ducts and cutting tables over 4 ft
wide as not only obstructions, but also as heat collectors. In some
situations the sprinklers may activate, sometimes they may not. We don't
know. 

Three things can happen in a fire situation: only sprinklers below the
cloud open, only sprinklers at the ceiling open or a combination of the
two. The first situation is unlikely and then only if conditions are
perfect. This would require a sprinkler under the cloud to activate and
cool the jet so insufficient heat makes it to the upper level to
activate additional sprinklers. The second scenario would be that if
none of the sprinklers below the clouds opened and only those at the
ceiling. This means you would effectively have a shielded fire,
developing away from sprinkler protection. If you look in NFPA 13,
shielded fires are classified under Extra Hazard Group II. The third
being a combination of ceiling and cloud sprinklers. This would be the
best case (short of no fire at all). Sprinkler below would attack the
fire at its origin and the ceiling would prevent it from spreading.
However, this would have a greater water demand.

Since we don't know which of the three scenarios are going to occur,
what would be the best course of action in design? If we calculate using
all sprinklers in the RA, then we have scenario 1 covered easily,
scenario #2 would give more water at the ceiling to address the shielded
fire issue and the design is based on scenario #3 so that is covered.

Just my thought process.





Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to