I think I'd argue with some of the presumptions in Todd's scenaria.
Why is a fire contained under a cloud least likely? The heads under
the cloud would be the first to be impinged and if you were not at the
edge of the of that 100 sqft or larger cloud I can see the jet being
cooled as it moves across the cloud. While I'd agree that some under
the cloud and some above the cloud is most likely we're still talking
less than all the design area above and below. All above is my least
vision but I am picturing clouds covering most of the room's
footprint. Even if this isn't the case we will have water from above
the cloud pouring off the edges of clouds breaking up the fire if it
crosses an opening and containing it to a perimeter, probably
substantially less than the design area if small clouds and definitely
so if large clouds. Picture this (and when this thread is exhausted
I'll share an informal interpretation if anyone is interested): Let's
say six ducts, each, say, 46" wide, running parallel, with a, say,
1/2" gap between them. Per NFPA do you need to sprinkler under them?
And since I'm bouncing around this topic we, myself included, spend a
lot of time on this forum speculating, guessing, logocizing (I think
that's a new word), etc. We do it for differing reasons, mostly
stemming from the rulebook not quite covering every way an architect
can figure out how to make our job difficult. So we get stuck with
Magic Pixie (I like that one and so will stick with that)
interpretations, both techs and engineers. We typically have a
solution we want and I'll use Bob as example since he started this
line of questioning. He was a hoping for a solution that went a
certain way. After Todd's argument of yesterday he resigned himself to
that approach but you could read between the lines that there was a
tone of defeat. After my argument he changed with a more uplifting
tone. Todd and I are jousting over this but neither of us are right or
wrong because of the Magic Pixie factor involved. My drivers are from
the standpoint of doing this academic thing for a dozen or so years.
I'm no longer informed viscerally by the realities of the marketplace
although I am quite aware and experienced in that reality. Todd is in
the maw daily and has that Damoclean Sword call PE hanging over his
head. Others have other demons informing their judgement and in this
issue we have only inference to guide us. I have a meeting so I'll
spare you all for the moment. And Cecil, if one of us can pull off
that stuff I sent you the other day we'll talk Champaign. We'll talk
anyway. Maybe August. And why am I on the totally ineffective 1031
Committee and not a 13 committee? This needs top be addressed to our
corporate overlords. All hail Caesar Moneybags, Oligarch of Monopoly
and the Shattered Economy.

On Tue, Mar 29, 2011 at 6:45 AM, Ronl.Fletcher <[email protected]> wrote:
> Cecil,
>
> Just out to curiosity do any of the models have the clouds hanging at an 
> angle, not parallel to the floor? Modeling and fire testing sounds like a 
> daunting task.
>
> Congrats on the grads.
>
> Ron Fletcher
> Aero Automatic
> Phoenix, AZ
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Sprinkler 
> Academy - C Bilbo
> Sent: Tuesday, March 29, 2011 6:17 AM
> To: FORUM
> Subject: RE: Cloud Calculations
>
>
> I am not sure where you guys have landed in this discussion, but wanted to 
> chime in with the latest work being done by the NFPA 13 Committee. And more 
> specifically, the work being done by the "Ceiling Cloud Task Group".  We have 
> begun the tough process of introducing changes to the standard that will 
> inlcude rules for ceiling clouds.  I gave a presentation to the Committee of 
> our task group's work at the ROP meeting in February.  The task group 
> includes the Chair, David Fuller from FM Global, and Steve Scandaliato, Mike 
> Meehan and others.  (Please, if you don't know who these people are, take a 
> miute to look them up.  It is awesome to know these folks!)
>
> As it currently stands, ceiling clouds are obstructions and require 
> sprinklers beneath (resulting in protection above and below).  The 
> calculations are only required to include one level of the sprinklers.  Both 
> are NOT requiredto be calculated together.  No addtional sprinklers from the 
> lower elevation are required to be included in the remote area at the deck. 
> And vice versa.  However, you would need to calculate both levels to 
> determine which is the most demanding area.
>
> We are asking the Research Foundation (NPRF) to sponsor testing of the 
> scenarios that Tom Wellen has modeled.  All of the Task Group's work starts 
> with Tom's models.  We have yet to come to any conclusions for the new rules. 
>  But we will likely have separate guidance in the 2013 edition for cloud 
> ceilings so that you will not always have to have sprinklers required above 
> and below and how one might have to calculate these scenarios. (the Academy 
> students got to draw some of the examples that we hope make it into the 
> standard...)
>
> And by the way..... the Academy ROCKS!!!  We are graduating our first 
> students next month.  Four folks will be getting their Associate's Degree in 
> Sprinkler System Technology from Parkland College!!  We are going to have one 
> serious party.  And you are all invited to come!  (Now, if I can just get Ron 
> Greenman to move to Champaign...)
>
>
> It should be recognized that the above is my opinion as a member of the NFPA, 
> and has not been processed as a formal interpretation in accordance with the 
> NFPA Regulations Governing Committee Projects and should therefore not be 
> considered, nor relied upon, as the official position of the the NFPA, nor 
> any of their technical committees.
>
>
> Sincerely,
>
>
> Cecil Bilbo
> Academy of Fire Sprinkler Technology
> Champaign, IL
> 217.607.0325
> www.sprinkleracademy.com
> [email protected]
>
> OUR STUDENTS SAVE LIVES!!
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to