Just check/consider spacing of both complements and go on from there.
We do a lot of schools and colleges; one of the most common upgrades to
high school and community college campuses over the past 2-3 years has
been performing arts buildings.   These are usually Type II shells with
suspended acoustical panels and a common dimensional increment for these
is 20', so if the water pressure is adequate we use EC on the clouds.
Sometimes the roof structure doesn't favor EC and it's not uncommon for
us to calc' both complements, just to be sure that we've got the more
demanding one.

Steve Leyton


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Bob
Knight
Sent: Tuesday, March 29, 2011 7:40 AM
To: [email protected]
Subject: RE: Cloud Calculations

So, now I'm really baffled.  If I follow this whole thread it seems that
the consensus would be one level calc'ed only verifying which level has
the greatest demand.  In my case the sprinklers at the ceiling will be
the greatest demand simply due to number and configuration of
sprinklers.  The clouds in this situation are running both perpendicular
and parallel to the branch lines.  Some of the clouds are rectangular
and up to 12' wide.  Other clouds are circular and have up to a 20'
diameter.  In all the clouds account for about 40% of the space.  All
the clouds have sprinklers beneath them.  

Thanks,

Bob K

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Ronl.Fletcher
Sent: Tuesday, March 29, 2011 7:45 AM
To: [email protected]
Subject: RE: Cloud Calculations

Cecil,

Just out to curiosity do any of the models have the clouds hanging at an
angle, not parallel to the floor? Modeling and fire testing sounds like
a daunting task.

Congrats on the grads.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Sprinkler
Academy - C Bilbo
Sent: Tuesday, March 29, 2011 6:17 AM
To: FORUM
Subject: RE: Cloud Calculations


I am not sure where you guys have landed in this discussion, but wanted
to chime in with the latest work being done by the NFPA 13 Committee.
And more specifically, the work being done by the "Ceiling Cloud Task
Group".  We have begun the tough process of introducing changes to the
standard that will inlcude rules for ceiling clouds.  I gave a
presentation to the Committee of our task group's work at the ROP
meeting in February.  The task group includes the Chair, David Fuller
from FM Global, and Steve Scandaliato, Mike Meehan and others.  (Please,
if you don't know who these people are, take a miute to look them up.
It is awesome to know these folks!)
 
As it currently stands, ceiling clouds are obstructions and require
sprinklers beneath (resulting in protection above and below).  The
calculations are only required to include one level of the sprinklers.
Both are NOT requiredto be calculated together.  No addtional sprinklers
from the lower elevation are required to be included in the remote area
at the deck. And vice versa.  However, you would need to calculate both
levels to determine which is the most demanding area.   
 
We are asking the Research Foundation (NPRF) to sponsor testing of the
scenarios that Tom Wellen has modeled.  All of the Task Group's work
starts with Tom's models.  We have yet to come to any conclusions for
the new rules.  But we will likely have separate guidance in the 2013
edition for cloud ceilings so that you will not always have to have
sprinklers required above and below and how one might have to calculate
these scenarios. (the Academy students got to draw some of the examples
that we hope make it into the standard...)

And by the way..... the Academy ROCKS!!!  We are graduating our first
students next month.  Four folks will be getting their Associate's
Degree in Sprinkler System Technology from Parkland College!!  We are
going to have one serious party.  And you are all invited to come!
(Now, if I can just get Ron Greenman to move to Champaign...)
 
 
It should be recognized that the above is my opinion as a member of the
NFPA, and has not been processed as a formal interpretation in
accordance with the NFPA Regulations Governing Committee Projects and
should therefore not be considered, nor relied upon, as the official
position of the the NFPA, nor any of their technical committees. 

 
Sincerely,


Cecil Bilbo 
Academy of Fire Sprinkler Technology
Champaign, IL
217.607.0325
www.sprinkleracademy.com
[email protected]
 
OUR STUDENTS SAVE LIVES!!

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to