Does it perform as solid shelving?  Yes, essentially, although there will be
some run-down.
Is it technically solid-shelving?  No.

The favorable factor to this scenario is the relative difficulty in igniting
2x6 lumber.
Would I protect as Class II in open shelved (cantilevered) racks?  Yes.
Flue space costs building owners money in unproductive floor.
Transverse flue space is essential to putting out rack fires.
If  you maintain 6 inch transverse flues (bolt the racks down that way or
install barriers)
   then 20' bays at your height should be OK.

scot deal
excelsior fire