I don't know if you have access to old Technical Updates, but this issue
was address a long time ago.

NFPA 13 (07) 7.2.6.5.1 only requires that the air maintenance device to
be listed.  The air compressor is only required to restore the normal
air pressure in the system within 30 minutes and is not required to be
listed.


Dale F. Wingard, SET
Design Manager
Triple "A" Fire Protection, Inc.
251.649.2034
[email protected]
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Justin
Scanlan
Sent: Friday, April 29, 2011 4:32 PM
To: [email protected]
Subject: U.L. air compressors


AHJ is not satisfied with UL listing on a tank air compressor bought
from a local hardware store. As I read the NFPA 13 3.2.3. concerning
equipment listing, it shall be "listed". This air compressor performs as
it should; however it is not listed for fire sprinkler use, as per AHJ.
So my question is this are nitrogen bottles listed for fire sprinkler
use as well as their regulators and hoses? Are all shop air compressors
listed for fire sprinkler use that we tap into? The UL listing on any
air compressor is valid? I didnt feel confident enough to challenge the
AHJ (Local Fire Captain) concerning these questions or my interpation of
codes. So what will the forum say?
 
Thank you for any input
Justin                                    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to