The air maintenance device needs to be listed but not the compressor. See
NFPA 13/2010 7.2.6.5.1 and A7.2.6.5.1. "Compressors are not air maintenance
devices and this section does not require compressors to be listed."

On Fri, Apr 29, 2011 at 2:45 PM, Ed Vining <[email protected]> wrote:

> It's late on a Friday afternoon, so you might not get a more authoritative
> answer.  Unless there has been a change, the compressor does not have to be
> listed.  It doesn't even have to be dedicated to the system.  In fact there
> doesn't have to be one.  I have seen one installation with several systems,
> and no power available.  Pressure was obtained from a wheeled gasoline
> powered compressor, toted from one system to the other as needed.
>
> You should wait until you get other responses before confronting the AHJ.
>
> Ed Vining
> 4819 John Muir Rd
> Martinez CA 94553
> 925-228-8792
> Cell 787-0465
>
>
> On Fri, Apr 29, 2011 at 2:32 PM, Justin Scanlan <[email protected]
> >wrote:
>
> >
> > AHJ is not satisfied with UL listing on a tank air compressor bought from
> a
> > local hardware store. As I read the NFPA 13 3.2.3. concerning equipment
> > listing, it shall be "listed". This air compressor performs as it should;
> > however it is not listed for fire sprinkler use, as per AHJ. So my
> question
> > is this are nitrogen bottles listed for fire sprinkler use as well as
> their
> > regulators and hoses? Are all shop air compressors listed for fire
> sprinkler
> > use that we tap into? The UL listing on any air compressor is valid? I
> didnt
> > feel confident enough to challenge the AHJ (Local Fire Captain)
> concerning
> > these questions or my interpation of codes. So what will the forum say?
> >
> > Thank you for any input
> > Justin
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to