The critical question has been answered - that being the compressor does not need to be Listed. I should say for Fire Protection use. When a listing is required, it does have to be for Fire Protection verses the slew of other listings available (often for electrical safety as likely performed on your compressor).

Roland

On Apr 29, 2011, at 2:32 PM, Justin Scanlan wrote:


AHJ is not satisfied with UL listing on a tank air compressor bought from a local hardware store. As I read the NFPA 13 3.2.3. concerning equipment listing, it shall be "listed". This air compressor performs as it should; however it is not listed for fire sprinkler use, as per AHJ. So my question is this are nitrogen bottles listed for fire sprinkler use as well as their regulators and hoses? Are all shop air compressors listed for fire sprinkler use that we tap into? The UL listing on any air compressor is valid? I didnt feel confident enough to challenge the AHJ (Local Fire Captain) concerning these questions or my interpation of codes. So what will the forum say?

Thank you for any input
Justin                                  
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to