Any hard data showing comparisons of dual/single hydrant testing out there? 

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Mark Sornsin
Sent: Friday, July 22, 2011 9:54 AM
To: [email protected]
Subject: RE: Convert Pitot to actual residual??

The residual pressure in a single hydrant test would be a bit lower, i.e. more 
conservative due to the friction losses incurred from the water moving up the 
hydrant barrel. The larger the flows, the less accurate (conservatively) the 
test becomes. 
I generally avoid these situations, but when you don't need a lot of flow for 
your design it is reasonably accurate (e.g. residential or light hazard designs 
for sure).

Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND 
Direct:    701. 280.8591 | www.ulteig.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, July 22, 2011 10:46 AM
To: '[email protected]'
Subject: RE: Convert pitot to actual residual??

My understanding is that single hydrant tests are not as accurate as double 
hydrant flow tests. You are trying to figure out how much pressure you can get 
from the system when it is discharging a certain amount of water. If you test 
the flowing hydrant, I imagine the pressure would read lower since the water 
would have a pretty high velocity. (just thinking out loud there... I have not 
researched it)

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Smith, Steven D. 
(CSFD)
Sent: Friday, July 22, 2011 10:41 AM
To: [email protected]
Subject: RE: Convert pitot to actual residual??

What if a pressure gauge was installed on the other outlet of  the hydrant from 
which the water is flowed and pitot reading is taken?

IOW, is it possible to have the test and flow hydrant one in the same?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Vince Sabolik
Sent: Friday, July 22, 2011 9:08 AM
To: [email protected]
Subject: Re: Convert pitot to actual residual??

Ron,

Ron,

Yeah figured so. I just thought that someone may have had one of those 'rule of 
thumb' thingys laying around.

Seems to me THAT should be possible, no?

I just wanted this to guestimate the design ahead of doing another test.

BTW, sorry about the double posts. I'm having an argument with me this morning.



At 10:58 AM 7/22/2011, you wrote:
>Vince,
>
>Since you don't have a residual, which is the left over energy in the
system
>measured in psi at the non-flowing hydrant, while flowing through that 
>circular orifice you're screwed and the test has to be re-done. Once
you
>have actual flow and residual you can calculate flow at any residual 
>pressure (changes with the size of orifice) or residual at any flow.
>Unfortunately static minus velocity (the pitot reading) doesn't equal 
>residual. Life and understanding the world would be so much easier if
it ran
>on magic and religion instead of physics.
>
>Vince Sabolik, West Tech Fire Protection, Inc.
11351 Pearl Road / Strongsville, Ohio 44136       440 
238-4800     Fax 440 238-4876
____________________________________________________________________


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to