You have one butt open with a great deal of turbulence going around the corner from the standpipe to the open butt while trying to take a static reading from the other side of the water column about 5" opposite. Not the best since the original static is really the residual for the entire pressure zone at that moment, and the residual is now the new static cum residual for that same system but with another source flowing.
On Fri, Jul 22, 2011 at 8:46 AM, Matt Grise <[email protected]> wrote: > My understanding is that single hydrant tests are not as accurate as double > hydrant flow tests. You are trying to figure out how much pressure you can > get from the system when it is discharging a certain amount of water. If you > test the flowing hydrant, I imagine the pressure would read lower since the > water would have a pretty high velocity. (just thinking out loud there... I > have not researched it) > > Matt Grisé PE*, LEED AP > Sales Engineer > Alliance Fire Protection > 130 w 9th Ave. > North Kansas City, MO 64116 > > *Licensed in KS & MO > > 913.888.0647 ph > 913.888.0618 f > 913.927.0222 cell > www. AFPsprink.com > > > -----Original Message----- > From: [email protected] [mailto: > [email protected]] On Behalf Of Smith, Steven D. > (CSFD) > Sent: Friday, July 22, 2011 10:41 AM > To: [email protected] > Subject: RE: Convert pitot to actual residual?? > > What if a pressure gauge was installed on the other outlet of the > hydrant from which the water is flowed and pitot reading is taken? > > IOW, is it possible to have the test and flow hydrant one in the same? > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Vince > Sabolik > Sent: Friday, July 22, 2011 9:08 AM > To: [email protected] > Subject: Re: Convert pitot to actual residual?? > > Ron, > > Ron, > > Yeah figured so. I just thought that someone may have had one of those > 'rule of thumb' thingys laying around. > > Seems to me THAT should be possible, no? > > I just wanted this to guestimate the design ahead of doing another test. > > BTW, sorry about the double posts. I'm having an argument with me this > morning. > > > > At 10:58 AM 7/22/2011, you wrote: > >Vince, > > > >Since you don't have a residual, which is the left over energy in the > system > >measured in psi at the non-flowing hydrant, while flowing through that > >circular orifice you're screwed and the test has to be re-done. Once > you > >have actual flow and residual you can calculate flow at any residual > >pressure (changes with the size of orifice) or residual at any flow. > >Unfortunately static minus velocity (the pitot reading) doesn't equal > >residual. Life and understanding the world would be so much easier if > it ran > >on magic and religion instead of physics. > > > >Vince Sabolik, West Tech Fire Protection, Inc. > 11351 Pearl Road / Strongsville, Ohio 44136 440 > 238-4800 Fax 440 238-4876 > ____________________________________________________________________ > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > -- Ron Greenman Instructor Fire Protection Engineering Technology Bates Technical College 1101 So. Yakima Ave. Tacoma, WA 98405 [email protected] http://www.bates.ctc.edu/fireprotection/ 253.680.7346 253.576.9700 (cell) Member: ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC They are happy men whose natures sort with their vocations. -Francis Bacon, essayist, philosopher, and statesman (1561-1626) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)