I think you should do the correct installation, regardless of what the PE 
shows. Bid it to install correctly, if you can't get a response from the PE 
prior to bid.

Most of those comments regarding transfer of liability would be chewed up and 
spit out by any half decent attorney. 


At 01:44 PM 10/5/2011, you wrote:
>I know this has been brought up before, but how are you handling 
>pre-engineered projects where they are not showing these specially listed 
>heads (Tyco CC1/CC2 or Viking COIN) as req'd per NFPA 13?  We are seeing 
>several of these again where there is a flat roof, less than 36" of clearance 
>between roof and ceiling and the PE is showing SSU sprinklers in the space.  
>These are projects that have been reviewed by the local AHJ and approved.  Do 
>you just install per the plan and say the responsibility is to some one else?  
>In this particular jurisdiction, even if the piping is installed per the 
>approved plans, the inspectors can and have required changes to the system to 
>correct plan review errors.  What if the project gets installed / inspected 
>per plan and there is a fire later on where the sprinkler system is not able 
>to contain the fire in the concealed space because of incorrect heads?  
>Where does the liability go?  One project in particular has the typical PE 
>comment: The installing contractor is to take full responsibility for 
>installing a system per NFPA 13 and shall add heads as needed at no additional 
>costs after bid.  Is this able to transfer liability to the contractor?
>
>One of my customers does a lot of multi-family type projects and we are seeing 
>this over and over.  I have been working with him to educate his GC's and the 
>architects / engineers on this issue, but there are still many projects that 
>come across his desk for bid like this.  Does anyone have a practical 
>solution?  We are trying to RFI these projects, but many times the PE will not 
>respond to the questions prior to the bid date.
>
>Sorry for the long run on questions.  Thanks in advance for your assistance.
>
>-- 
>Please feel free to call if you have any questions or comments.
>
>Sincerely,
>
>Travis Mack, SET
>MFP Design, LLC
>2508 E Lodgepole Drive
>Gilbert, AZ 85298
>Office (480) 505-9271
>Fax (866) 430-6107
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to