Methanol is miscible but is also lighter than water.  Foam-water systems are 
usually preferred due to their ability to blanket the material and reduce the 
vapor release which is of significant concern.  If you use water alone it's 
going to take considerably more water than if you use a foam-water system.  Do 
you have an adequate water supply?

One thing to find out is exactly what you are dealing with in terms of the 
contaminated methanol.  Since you know the end product is pure methanol, you 
may have other issues with the incoming material.   

The problem with water only when dealing with alcohols is some can still be 
flammable when mixed with water, you would have to know the dilution point 
where the mixture is no longer flammable.  Again, another reason to blanket the 
material.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Monday, January 24, 2011 6:42 PM
To: [email protected]
Subject: Methanol Building

I'm looking at providing fire protection for a building (approx. 25' x 10' x
16' high), being used to purify methanol from a contaminated source. Has
anyone come across using a standard wet system for this type of application
before? What other system have been used? Any input will be appreciated.

Tony  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to