George, I don't like being above the second floor because I don't trust the
sprinkler guys. I'm likely to become a ground floor guy only. I had to jump
off my garage roof this past summer (ladder mishap) and the impact at 62 is
far more severe than I remember at 32. Thank god the army taught me how to
fall out of an airplane.

On Wed, Oct 5, 2011 at 11:22 AM, George Church <[email protected]>wrote:

> I know we don't have time to bid it once, but doing a base bid for what's
> shown, and an ADDER for the CC2's with a description like "required to meet
> code" and if they accept it, you and they are covered.
> If they don't, then at least you have the leg to stand on that you educated
> them on what was needed, they declined to pay for it, and thereby
> (financially) directed you to proceed with the installation according to
> (defective) plans and specs.
>
> Another way is to call the AHJ as you submit and inform him that your
> submittal doesn't meet code. When the dwgs are bounced, send a COR for the
> redesign time, schedule impact, and the original ADDER from your bid and ask
> for the extra again.
> This puts them in the position of delaying the project, knowing they can't
> get a CO without sprinkler, and that your schedule impact will grow larger
> by the day.
>
> It might also be worth pointing out to the GC or Owner you're working for
> that the PE that incorrectly designed it without the CC2s has liability
> insurance to cover the cost of fixing his mistakes- and this would be one of
> them.
>
> If we as an industry held their feet to the fire, we'd have less plumbing
> designers burping out faulty designs. If they didn't shape up, Victor O
> would, in rate premiums or withholding coverage, enforce compliance with
> practicing within their area of competence.
>
>
> Boy, I sure hope bridge and tunnel construction doesn't have this same
> thing happening behind the scenes. I've stopped feeling comfortable being
> above the 4th floor years ago, knowing elevator inspectors are likely just
> as sharp as DOH and our local  inspectors.
>
>
> George L.  Church, Jr., CET
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Travis Mack, SET
> Sent: Wednesday, October 05, 2011 1:45 PM
> To: [email protected]
> Subject: Combustible Concealed Spaces
>
> I know this has been brought up before, but how are you handling
> pre-engineered projects where they are not showing these specially listed
> heads (Tyco CC1/CC2 or Viking COIN) as req'd per NFPA 13?  We are seeing
> several of these again where there is a flat roof, less than 36"
> of clearance between roof and ceiling and the PE is showing SSU sprinklers
> in the space.  These are projects that have been reviewed by the local AHJ
> and approved.  Do you just install per the plan and say the responsibility
> is to some one else?  In this particular jurisdiction, even if the piping is
> installed per the approved plans, the inspectors can and have required
> changes to the system to correct plan review errors.  What if the project
> gets installed / inspected per plan and there is a fire later on where the
> sprinkler system is not able to contain the fire in the concealed space
> because of incorrect heads?
> Where does the liability go?  One project in particular has the typical PE
> comment: The installing contractor is to take full responsibility for
> installing a system per NFPA 13 and shall add heads as needed at no
> additional costs after bid.  Is this able to transfer liability to the
> contractor?
>
> One of my customers does a lot of multi-family type projects and we are
> seeing this over and over.  I have been working with him to educate his GC's
> and the architects / engineers on this issue, but there are still many
> projects that come across his desk for bid like this.  Does anyone have a
> practical solution?  We are trying to RFI these projects, but many times the
> PE will not respond to the questions prior to the bid date.
>
> Sorry for the long run on questions.  Thanks in advance for your
> assistance.
>
> --
> Please feel free to call if you have any questions or comments.
>
> Sincerely,
>
> Travis Mack, SET
> MFP Design, LLC
> 2508 E Lodgepole Drive
> Gilbert, AZ 85298
> Office (480) 505-9271
> Fax (866) 430-6107
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon,
essayist, philosopher, and statesman (1561-1626)
-------------- next part --------------
An HTML attachment was scrubbed...
URL: 
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20111005/0f7941c4/attachment.html>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to